RCBO tripping next door RCBO | on ElectriciansForums

Discuss RCBO tripping next door RCBO in the UK Electrical Forum area at ElectriciansForums.net

Joined
May 20, 2009
Messages
241
Reaction score
33
Location
Minnions
Testing an RCD on one rfc upstairs tripped the upstairs and downstairs circuis, which was the RCBO next door to it. Turned off the power to all circuits tested downstairs RCBO on its own RCD failed 1x and 5x tests. Disconnected conductors from this RCBO tested RCD at the board worked ok. Put cables back in failed RCD tests. Removed every fuse from every fuse spur and disconnected all plugs etc. Tested ok. Put all the fuses back and all plugs switched on tested again all ok. went upstairs tested rcbo tripped individually. madness ?
 
come again ,take a pic to see what you have got on the c/u.

I think I forgot a few full stops. The RCBO failed RCD test.

I'm confused, is it now fixed?

I’m still confused lol once I’d disconnected everything on the circuit the RCBO passed the RCD tests. Before that it was only passing if I disconnected the conductors from the RCBO.
 
I’m still confused lol once I’d disconnected everything on the circuit the RCBO passed the RCD tests.

Before that it was only passing if I disconnected the conductors from the RCBO.
Before that it was only passing
was it passing when you tested it with out the circuits being on or off .;)
 
topic title somewhat misleading in this context, i.e. "next door"

When I say next door I mean in the box.

was it passing when you tested it with out the circuits being on or off .;)

This occurred when I auto rcd tested upstairs RCBO sockets ‭which was tripping both upstairs and downstairs. The first time I got the Rcbo to pass was when I disconnected all other circuits and disconnected the conductors from the rcbo and rcd tested at the origin.
 
Polarity in accessories, did you do an R1R2 and test every point? Not sure if that would cause your issues!
 
Seen some people on here talk about N-E faults causing a RCD to stop operating, never seen it myself but I sure someone else will be able to explain.

Have you tried an insulation resistance test between the two circuits with them disconnected from DB? Perhaps you have a bit of a short between the 2 circuits if they are causing each others RCBO's to operate. Cable burns from installation maybe.
 
"Removed every fuse from every fuse spur and disconnected all plugs etc. Tested ok"
So with all loads removed the circuit tested ok?
Could one of the appliances be leaking DC or not compatible with an AC type RCBO (assuming it is an AC type RCBO)
 

Reply to RCBO tripping next door RCBO in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
387
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
693
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top