Discuss Rcbo tripping on 1/2 settings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Always taught to test on no-load!any thoughts on this
The load is causing some leakage that, when added to your MFT's In/2 test current, takes it above the trip threshold.Rcbo tripping on 1/2 settings with load connected but ok when load disconnected
Always taught to test on no-load!
I have found this to be a flawed concept as how do you differentiate between a spurious result and a faultGuidance Note 3 indicates RCD testing should be carried out with the load disconnected to avoid spurious results.
It's actually quite simple - you drag a wall chaser through an illogically buried live cable that is out of zones and see whether the RCD beats the MCB, and whether you get a 30ma jolt or get thrown across the room. (I'm told)I have found this to be a flawed concept as how do you differentiate between a spurious result and a fault
I must have missed that test in GN3It's actually quite simple - you drag a wall chaser through an illogically buried live cable that is out of zones and see whether the RCD beats the MCB, and whether you get a 30ma jolt or get thrown across the room. (I'm told)
As I mentioned in an earlier post I've found many odd results and replaced a few RCD's some only months old and now I take a more cautioned approach given the reliance many people place on an RCD / RCBOBut seriously, after managing to keep all my limbs I tested everything again. This showed the RCD behaved with no loads but was considerably slower with loads connected. I replaced the RCD and normality returned.
When I first had this issue I took the decision to delve a bit deeper having only fitted the CU 6 months prior and knowing that a test at a point on the circuit tripped the RCD at the time and now didn't I decided to test as GN3 suggests you should at the CU with the circuit disconnected when it tripped within the time limits I wanted to find out why so did the ramp test at the CU and found the RCD tripping about 6 - 7 mA over the 30mA limitThis was a few months ago and I've been reflecting ever since that the installation would have passed an EICR with acceptable results even though the RCD was not within spec. I actually think GN3 needs reconsidering. 'What actually happens' surely matters more than 'what might/should theoretically happen'.
I routinely ramp test all RCD's / RCBO's since I found this problem and note the results on an EIC / EICR / MEWC.I'd like to think that it's rare than no-load tests and real world tests differ in outcomes, but unless we start routinely trying this, how would we know the scale of the problem?