Verify the rcbo is wired correctly at the consumer unit
Does your installation not have a local lighting circuit?
Is the rcbo necessary for this installation and if so why
Verify the continuity of the circuit cpc by carrying out the R1+R2 continuity test with your low ohms meter
Insulation resistance test the circuit for the smokes,taking care that sensitive electronic equipment has been disconnected
Make sure you have verified polarity of the smokes before energising
If the circuit itself is sound,test the Rcbo with your Rcd tester to see if it is tripping within the parameters of a 30 m/amp rcbo,if that is the rating you have used
There that should sort it out