anyone got any ideas on this.

Had to change a lighting circuit mcb to an rcbo due to cable we put into the wall (work is on a school). The old mcb was 15amp rated and 1.5mm twin and earth circuit. I changed the mcb to a 10amp RCBO but when I tried to turn on it tripped. so I thought it could of been tripping due to overloaded, I then changed the RCBO to a 10amp MCB and it was fine so no overloading. I then went around disconnecting the outside emergancy lights and trying to reset the RCBO. Got the first one on with the rest disconnected but when it came to the secound light it tripped. Byepassed the second onto the third and still tripped, then I disconnected the first light byepassing it and put the secound one on with the rest off it stayed in. Its like everytime a light is added it trips as if overloaded. the RCBO was type C as well any thoughts on this.

thanks
 
earth leakage on emergency lights. probably due to the electronics in them. each one will have a small leakage, but add all together and it takes the rcbo over it's threshold. try a ramp test with no load, then do it again with as many lights conneced as don't trip it. you'll probably see the trip current much lower.
 
I would ramp test the RCBO first as Tel has mentioned as it could be faulty on the RCD side of it.

If this proves OK a IR test on your cct to make sure it is sound for the RCD to hold. It should hold above 7666 Ohms with a 30mA unit. (230/0.03)

You could try clamping the cct with a Earth leakage clamp meter but this a IR test should be done and you will require the readings for the paperwork!
 

Reply to rcbo tripping in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
842
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
965

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
686
davesparks
D
  • Question
And exciting when that Hager AFDD finally tripped 😂
2
Replies
28
Views
2K
nicebutdim
N

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top