Rcbo with higher than permitted zs | on ElectriciansForums

Discuss Rcbo with higher than permitted zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Joined
Dec 10, 2019
Messages
33
Reaction score
11
Location
Scottish Highlands
Hi I was testing a large holiday let property which has a three phase supply and dB
Now the original install was in 2012 and electrically is well done but poorly designs on socket circuits all rcbo are type c and only on socket circuits I am over the max permitted zs I would recommend change to type b but looking for some regulation to note on test cert
 
You can disconnect on the RCD side of the RCBO to meet the regulations, as you generally have to for a TT system.

I would generally prefer to meet disconnection on the OCPD side of things on TN systems if at all practical, just as i believe the thermal-magnetic trip side is simpler and more reliable than the RCD electronics. But it is not an absolute must.

How far off meeting Zs are you?

Do you know if there are any other reasons for putting the sockets on C-curve breakers, such as it is used for motor loads with high start-up currents?
 
Last edited:
In terms of the regs, 411.4.5 states you can use an RCD to meet ADS.

411.4.204 covers the Zs requirement by citing Table 41.5 (which is basically 50V/In but not adding 200 ohm as max stable value)
 
You can disconnect on the RCD side of the RCBO to meet the regulations, as you generally have to for a TT system.

I would generally prefer to meet disconnection on the OCPD side of things on TN systems if at all practical, just as i believe the thermal-magnetic trip side is simpler and more reliable than the RCD electronics. But it is not an absolute must.

How far off meeting Zs are you?

Do you know if there are any other reasons for putting the sockets on C-curve breakers, such as it is used for motor loads with high start-up currents?
Thanks for the replay
Supply is a tncs with a ze of 0.15
At 250v
No just standerd domestic items realty on socket most socket circuits
Exsept garage has a small pump for the private water supply I think that's all that was available for rcbo at the time of install for the crabtree distribution board and looks like the electrician who designed the installation made poor choice of that equipment
Of the top of my head one socket circuit zs was 0.83
 
Thanks for the replay
Supply is a tncs with a ze of 0.15
At 250v
No just standerd domestic items realty on socket most socket circuits
Exsept garage has a small pump for the private water supply I think that's all that was available for rcbo at the time of install for the crabtree distribution board and looks like the electrician who designed the installation made poor choice of that equipment
Of the top of my head one socket circuit zs was 0.83
Also no rcd uplift I use a Megger 1721
And high quality crabtree rcbo from 2012
 
Of the top of my head one socket circuit zs was 0.83
With Ze = 0.15 you have R1+R2 of around 0.68

Assuming 2.5mm T&E radial is 19.5 ohm/km then you are looking at around 35m length, so it a sane result, but in that case it ought to be on 20A which as maz Zs of 0.87 ohm so met?

If it was a typical 32A RFC on 2.5mm then r1+r2 = 4 * (R1+R2) so about 140m which is fairly long.

It is not big issue but may suggest something else is not quite right?
 
Also no rcd uplift I use a Megger 1721
And high quality crabtree rcbo from 2012
All dead R1 R2 an
With Ze = 0.15 you have R1+R2 of around 0.68

Assuming 2.5mm T&E radial is 19.5 ohm/km then you are looking at around 35m length, so it a sane result, but in that case it ought to be on 20A which as maz Zs of 0.87 ohm so met?

If it was a typical 32A RFC on 2.5mm then r1+r2 = 4 * (R1+R2) so about 140m which is fairly long.

It is not big issue but may suggest something else is not quite right?
It is a massive property and and every other test is consistent most of circuits would be fine on a 20 amp rcbo apart from kitchen i just think it was poorly designed in the first place. For example there is a 50 amp rcbo feeding 25mm swa to the annex / garage with a 14 way high integrity d.b with 4x rcbo and 2 X rcd and rest MCB
 
It probably was poorly designed but when it comes to testing it is what it is. Although not in your case a high Ze may leave you with no choice but to rely on an rcbo for fault protection I personally wouldn't look into it too deeply.
 
Yes, not very good design but equally not dangerous.

The Zs is higher than UK regs on OCPD alone but given your 32A C-curve trip range for 230V covers Zs = 1.1*230/(5*32) = 1.58 ohms best-case down to 0.8 * 0.95 * 230 / (10 * 32) = 0.54 ohms worst-case, your measured 0.83 is going to be met for over half the tolerance range, and the RCD side always met.
 
Agree, with the Rcd in circuit, R1+R2 tests, its compliant not ideal but ok.
The worry I have these days is that the lesser experience electricians, we’ve a high Zs reading put a Rcd on it.
Without the relevant tests it’s a major concern, days gone by you would certainly fix the problem
 
Agree, with the Rcd in circuit, R1+R2 tests, its compliant not ideal but ok.
The worry I have these days is that the lesser experience electricians, we’ve a high Zs reading put a Rcd on it.
Without the relevant tests it’s a major concern, days gone by you would certainly fix the problem
Exactly, if it is just a rather long cable then it is not so serious, even though it is probably not meeting the VD spec either. But it could be something more serious that ought to be fixed (bad joint, etc) and not simply side-stepped with the RCD aspect.
 
Thank you all so much for the replies
And sorry for late response I'm working away at the moment and haven't had much time or that good internet connection I had noted on cert that it was a poor design and there is a few other issues I am due to go back and rectify once I am working back local thanks again the collective hive mind
 

Reply to Rcbo with higher than permitted zs in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
839

Similar threads

  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O
  • Question
All the lamp post cutouts I've ever seen have a twin swa gland plate built in to the base.
Replies
2
Views
634
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top