testing a 40A rcbo on a shower today and got >400ms at x1 is the rcbo knackered i removed the load and tested it and it still did it, i dont want to get another 1 and it do the same thing.
IR was >299Mohm
Zs 0.16
Ze 0.11
Looks like the RCBO is operating right at its limits ,x1 should be <200 ms , could be a good idea to replace it
check you,r tester is not set to 10ma. i have done this. wont trip on 1x will trip on 5x. wasted an hour like this. doh!!!