If a board is fitted with all RCBO's would a borrowed neutral show up and cause any problems? I reckon not but a mate of mine reckons it would cause trippng ??
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss RCBO's and borrowed neutrals in the Australia area at ElectriciansForums.net
yes it would if a neutral shares between 2 circuits protected by 2 RCBO's then you find that both of the RCBO's will trip when a load is applied ,if this is the case most commonly in lighting circuits you need to identify which circuits have a shared or borrowed neutral by a process of elimination and testing
It's not about where the neutral ends up, it's the path that it takes to get there!
For a 30mA RCD or RCBO, the current going out down the line and returning down the neutral must be equal - if the imbalance exceeds 30mA it will trip.
So:
If your line current goes back to another neutral, you have an imbalance in both circuits - and if both are RCD'd, both RCDs will likely trip (though with something like a clock radio only drawing a few mA, maybe only one will trip)
Even though RCBOs are single pole devices in terms of overcurrent, switching and isolation, in order to work the neutral current for that circuit MUST flow through the toroid inside, so that the (hopefully) equal and opposite currents result in no current being applied to the trip solenoid.
simon.