Hello. Just a quick question, when using RCBOs in a TT system does the max permitted Zs change? For example the max permitted Zs for a 32a type c RCBO in a TN system is 0.68, does this change to 1667 in a TT system?
 
or in fact, NO!
it is 1667 on any earthing system I can think of other than something a bit special like some IT
(independent of terra, not Information Technology!!)

@default May the force be with you. :tearsofjoy:

How about one that has only mcbs ? aka yoda. :)
 

Reply to the thread, titled "RCBOs and TT systems" which is posted in UK Electrical Forum on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
Colchester
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
RCBOs and TT systems
Prefix
UK 
Forum
UK Electrical Forum
Start date
Last reply date
Replies
6

Thread Tags

Thread statistics

Created
default,
Last reply from
mainline,
Replies
6
Views
120
Back
Top