Hi all,
Did a CU change today, now have 9 circuits are on 30ma RCBO's
A TNCS property with a ZE of 0.35........
16mm MEC
10mm bonding to gas and water
CU was from the Denmans basics range 12 way
Now all the RCBO's trip fine on when you test them x1 and x5, and when I did a ramp test they all tripped at around 23ma
But when I did a high current ZS test directly on the RCBO they no trip. They were all the same.
So I tried the upstairs and downstairs power at various socket..Still no trip on any of them
I have read a post from Sintra some time ago when he had a similar prob but there was no solution
any advice greatly appreciated.
Meter appears to be ok as it trips the RCD in my MK Sentry board at home!!
G :sad_smile: