S

sliver

I seem to be having alot of trouble after installing anew consumer unit with 5 RCBO's I have got really high milli second readings and dont understand why I am looking at 350 x 1 and no operation on x 5. IR is fine and so is R1 + R2. Any suggestions????:confused:
 
Check the size of your main MET and check your Ze if the main MET is to small or poor connection this will give you those sort of problems.
 
thanks for the reply mike. i've a rod which is installed beneath the lounge floor and am getting a reading of 56ohms .i've the possiblity of pme which will bring it down to 0.35,but am concerned that there may be a borrowed neutral on one of the old circuits,will this be a factor to effect newly installed circuits??
 
Borrowed neutral's usually take an RCD out as soon as you power up, have you tried swapping the Rcbo's around ( where the amps are the same ) to see if it's a duff rcbo?

Lee
 
thanks lee,i've got a problem that when the bathroom lighting is energised the rcbo trips out,so i think that is where the neutrel problem lies,but yes i,ve swaped ,and also installed other rcbo's to double check readings from the original onesand they come up with the same reading.thanks for the input the more views i can get on this the easier to solve for me
 
It probably is borrowed neutral. Some people have a habit of nicking the neutral from a shower feed to feed a light over the shower. If you have the choice of type of supply go for pme.
 
It probably is borrowed neutral. Some people have a habit of nicking the neutral from a shower feed to feed a light over the shower. If you have the choice of type of supply go for pme.
hi do you have up and down stairs lighting this seems to be the most likely
place to find borrowed neutral
 

Reply to RCBO's on to old wiring....HELP!!! in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
252
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
724
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
696

Similar threads

He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
602
The actual listed observations seem easily resolvable, comfortably less than a day's work. The picture of the supply poses a few questions...
Replies
5
Views
993

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top