RCBOs vs RCDs Pt2 | Page 4 | on ElectriciansForums

Discuss RCBOs vs RCDs Pt2 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

I understand perfectly well thankyou, I'm not sure you do.

Neutral current from the whole installation diverts through an N-E fault on a circuit.

Current does not normally flow through a cpc
 
Makes you wonder how we ever managed to get by before the introduction of RCD's, or even before MCB's/MCCB's when fuses were basically the sole means of protection from Main switchboards all the way down to final circuits....

OK, maybe on main switchboards, they could well of had early earth fault relay protection, but then we wouldn't be talking in terms of 30mA or anything close to it!!

Perhaps N-E faults didn't exist in those days!!...lol!!
 
We got by fine without them, just as we can get by fine without them today if we insisted on better installation standards and stopped treating RCDs as a one size fits all soloution to poor installation work.

Of course neutral faults have always existed, and they will always occur.
But was TNCS, and particularly the PME subdivision of it, so common in those days?

My issue is with the concept of a device which detects a fault on the neutral then reacts by disconnecting the live.
Yes it satisfies bs7671 in terms of protection, but isn't bs7671 supposed to be the minimum standard of acceptability rather than the be all and end all.
 
We got by fine without them, just as we can get by fine without them today if we insisted on better installation standards and stopped treating RCDs as a one size fits all soloution to poor installation work.

Of course neutral faults have always existed, and they will always occur.
But was TNCS, and particularly the PME subdivision of it, so common in those days?

My issue is with the concept of a device which detects a fault on the neutral then reacts by disconnecting the live.
Yes it satisfies bs7671 in terms of protection, but isn't bs7671 supposed to be the minimum standard of acceptability rather than the be all and end all.

I'm all for SP+N RCBO's, but as i've stated the present standard SP RCBO's aren't all doom and gloom, they are providing a perfectly acceptable means of additional protection to SP circuits.

Public distribution PME supplies have been around for a lot longer than most imagine, certainly from the middle 1940's with a big expansion in the 50's, 60's, 70's especially in the semi rural areas on the outskirts of towns etc...
 
SP RCBOs are acceptable yes, but when better options are available for the same price I see no reason to use them in a new board.

Obviously adding or altering a single circuit in an existing board you work with what is there already and if that means fitting SP RCBOs then so be it
 
None of which really matters if the RCBO is simply used as an MCB with additional protection.

What on earth are you talking about?

If an mcb is needed you use it as an mcb.

If RCD protection is needed in addition you either install an RCCB before or after the mcb or an RCBO to provide both functions in one.

Whatever reason you install an RCBO for then if it is SP it will detect N-E faults and not disconnect them, it will disconnect the L.

Several cans of worms opened here!!
Personally I think you are over thinking it.
There are countless installations with N-E faults working only on OCPD's not going up in smoke.
An RCBO is normally added to OCPD only installations as a replacement for an MCB but with the benefit of additional protection where bs7671 requires it.

Thats what I'm talking about.
 

Reply to RCBOs vs RCDs Pt2 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
732
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
972

Similar threads

  • Question
Leaves the potential nuisance of knocking off a raft of equipment unnecessarily
Replies
7
Views
1K
Interesting. Did you ever resolve this?
Replies
10
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top