When replacing a light housing, I found the RCCB was somehow tripped. I first used a pen tester to check the wires and found them normal (no voltage). I then used a multimeter to test again. Here are the results:

L-N 7.4 v
L-E 6.8 v
N-E 3 V

After the RCCB was tripped, the readings were zero. So, I think the readings were real.
Only N-E would trip the RCCB, other combinations wouldn't.

Any guess what's going on here?
 
The RCCB detects an imbalance in current between the L & N. It does not matter if that is due to a L-E fault or a N-E fault.

The former is usually more dangerous as it could be someone getting an electric shock, the latter is not as common (less chance of poor insulation breaking down due to low voltages) but is often responsible for difficult to find spurious trips of RCD as systems with a normally very low N-E difference might only see enough stray imbalance current on the occasional heavy load.
 
I think the OP is probably asking why there were some voltages measured on a 'dead' cable and how come that same 'dead' cable could trip a RCCB?

There's a few things about why you got some readings, but firstly you need to know that you NEVER rely on a pen stick for safe isolation!

The most likely reason that there were a few odd volts here and there is because there were - either through what we call induced voltage (commonly seen on two way lighting circuits and where multiple cables run along each other) and/or the switch itself is not fully isolating/internal arcing. MCB's tend to have a larger internal gap space than a 50p faceplate switch.

There is normally always something floating around on what you perceive as a 'dead' neutral unless it's actually been fully disconnected (or is via a two-pole isolator which is unusual in a domestic situation) and so as others have said, the RCCB has enough to compare the two and will disconnect.
 
The thing to remember is that 'isolating' a circuit using the circuit breaker only disconnects the live. The neutral is still connected and the RCD or RCCB is monitoring the neutral, hence the tripping you experienced. I'm not sure of the definitions written in the UK regs but I wouldn't normally consider a circuit to be fully isolated if it was just switched off by an MCB.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Myanmar
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
All Other Countries (This Is English Speaking Website Only - WE don't mind Google Translate Users :)
What type of forum member are you?
DIY or Homeowner (Perhaps seeking pro advice, or an electrician)

Thread Information

Title
RCCB tripped when neutral - earth touching
Prefix
N/A
Forum
DIY Electrical Advice
Start date
Last reply date
Replies
7

Advert

Thread statistics

Created
winayetun,
Last reply from
Marvo,
Replies
7
Views
6,533

Advert

Back
Top