A

adam1984

Afternoon all.

This is a weird one but I thought i would ask your thoughts to satisfy my own cuisosity and apologies for long post!

Board is a Crabtree with 1no RCCB. The RCCB tripped when the TV was plugged in and socket turned on. RCCB would not instantly re-set but it did after a couple of minute.

The RCCB supplied: Downstairs power, Upstairs Power, kitchen, Extension, utility/boiler (5mcbs)

So I reset RCCB. Go back to "TV Socket", plug in Martindale socket tester, switch on socket switch and RCCB trips (do this a couple more times and keeps tripping) The TV socket is on Downstairs power MCB.

Homewoner says that its normally the tumble dryer / kettle / microwave (on the utility MCB) that ususally trips the RCCB but once reset they work again.

Reset RCCB and and all MCB's are in the ON position. Go to utility room and plug Martindale socket tester into socket, switch on and RCCB trips again. I try several different sockets and trips every time however when the boiler is fired up it doe not trip the RCCB.

If I turn off the MCB to the Utility room and try my Martindale socket tester in the kitchen sockets then it trips the RCCB. If i turn off the the Extension and utility / boiler MCB then the "TV Socket" does not trip the RCCB and nieither do the kitchen sockets.

Now the extension is actually a 2 storey extension but when I turn this MCB off it only turns the power off to the downstair extension (granted the upstairs may have been taken off the upstairs power)

I took off every socket face on the affected circuits and wiring all looked fine. I checked all cables where possible (ones clipped direct etc) for signs of damage. I asked the homewoner if they have done any DIY recently. I checked all outside equipment for signs of water ingress or damage and everything I checked looked ok and no signs of damage.

The homeowner has lived in the house for approx 4 years and on the face of it it is really modern and had a massive refurb job done by the previous owners but the current homeowner has said they have had quite a lot of problems with te house and especially with the electrics.

I think that there is a dodgy conection somewhere but I couldnt find it so must be burried in / behind a wall somewhere.The junction boxes I found were wired ok. Anyone shed some light on what they think it may be? Ways in which you would try and trace fault? No insulation resistance test was carried out.
 
IR test. ramp test ( both with circuits connected and not connected ). earth leakage clamp meter round the tails. before that's done we're guessing.
 
Sounds like its time to get the proper test gear out and go through the usuals, should pick it up fairly quickly!

Probably throw the martindale socket tester in the bin as well.
 
Back to basics! Get the insulation res testing done, circuit by circuit. You need to break down the installation into its individual circuits, id what's good and what's not; rcd tests etc and work from there. It takes the time it takes.

Darn, these two ^^^^ are fast posters!
 
The issues that you state sound very much like IR leakage on either circuits or appliances , have you not done ANY testing of the circuits at all , as already mentioned this would have been the first thing to do ....
 
Thank you for your replies.No testing was done

The thing that is puzzling me is that the boiler would not trip the RCD but the utility room sockets do and they are on the same MCB.


Also the kitchen sockets would trip the RCD when the extension and utility room MCB's are on but when I turned off the Extension and Utility room MCB's the kitchen sockets would not trip the RCD.

Also everything was unpluged and the Martindale alone would trp the RCD.

Testing procedure duly noted.
 
Thank you for your replies.No testing was done

The thing that is puzzling me is that the boiler would not trip the RCD but the utility room sockets do and they are on the same MCB.


Also the kitchen sockets would trip the RCD when the extension and utility room MCB's are on but when I turned off the Extension and Utility room MCB's the kitchen sockets would not trip the RCD.

Also everything was unpluged and the Martindale alone would trp the RCD.

Testing procedure duly noted.

Dont mean to be horrible mate but you cant sort this problem with a socket tester.
 
Basically your martindale is not suitable for this fault. Even though you are switching MCB's the neutrals are still all connected together so you would need to separate to determine which circuit has the fault and then go from there. You need an insulation resistance tester minimum and preferably a earth leakage clamp meter as well to fault find this effectively.
 
Afternoon all.

This is a weird one but I thought i would ask your thoughts to satisfy my own cuisosity and apologies for long post!

Board is a Crabtree with 1no RCCB. The RCCB tripped when the TV was plugged in and socket turned on. RCCB would not instantly re-set but it did after a couple of minute.

The RCCB supplied: Downstairs power, Upstairs Power, kitchen, Extension, utility/boiler (5mcbs)

So I reset RCCB. Go back to "TV Socket", plug in Martindale socket tester, switch on socket switch and RCCB trips (do this a couple more times and keeps tripping) The TV socket is on Downstairs power MCB.

Homewoner says that its normally the tumble dryer / kettle / microwave (on the utility MCB) that ususally trips the RCCB but once reset they work again.

Reset RCCB and and all MCB's are in the ON position. Go to utility room and plug Martindale socket tester into socket, switch on and RCCB trips again. I try several different sockets and trips every time however when the boiler is fired up it doe not trip the RCCB.

If I turn off the MCB to the Utility room and try my Martindale socket tester in the kitchen sockets then it trips the RCCB. If i turn off the the Extension and utility / boiler MCB then the "TV Socket" does not trip the RCCB and nieither do the kitchen sockets.

Now the extension is actually a 2 storey extension but when I turn this MCB off it only turns the power off to the downstair extension (granted the upstairs may have been taken off the upstairs power)

I took off every socket face on the affected circuits and wiring all looked fine. I checked all cables where possible (ones clipped direct etc) for signs of damage. I asked the homewoner if they have done any DIY recently. I checked all outside equipment for signs of water ingress or damage and everything I checked looked ok and no signs of damage.

The homeowner has lived in the house for approx 4 years and on the face of it it is really modern and had a massive refurb job done by the previous owners but the current homeowner has said they have had quite a lot of problems with te house and especially with the electrics.

I think that there is a dodgy conection somewhere but I couldnt find it so must be burried in / behind a wall somewhere.The junction boxes I found were wired ok. Anyone shed some light on what they think it may be? Ways in which you would try and trace fault? No insulation resistance test was carried out.

That would be the FIRST thing I would do. Unplug vunerable equipment only,leave the rest and do a global LN-E IR test,you cant possibly rectify an RCD tripping fault without first confirming satisfactory IR readings.
Are you actually charging someone for this....?
 
Apologies, the reason I am mentioning the socket tester was to say that even that was tripping the RCD with everything unplugged (My theory being that this isn't a big load)

The homeowner was not charged for me being there.
 
By the description supplied , I very much doubt the OP knows how an RCD actually works and the fault it detects , and because of this the testing has not been done before actually asking this question here...
 
Here we go with the "I'm bigger and better than you" playground antics. I came here to ask advice / thoughts on what would be the way in which you would have dealt with this. Experience is what is required in this situation but how do I go about getting that? I didn't charge the customer, left them in a better situation then when I walked in the door and explained that they needed someone with the time and experience to deal with their situation.
 
Please don't conduct an IR test.
It wouldn't be fair on the home owner.
You need to stop, ask an experienced electrician for there help, and learn from there actions.
I am not being unkind or un-helpful.
I am giving you sound advise before you either damage something, become very frustrated, or end up falling out with the home owner because they will eventually become suspicious of your lack of knowledge, and level of experience.
Your going for a stroll into the Amazon jungle, and you will get lost.
 
Afternoon all.

This is a weird one but I thought i would ask your thoughts to satisfy my own cuisosity and apologies for long post!

Board is a Crabtree with 1no RCCB. The RCCB tripped when the TV was plugged in and socket turned on. RCCB would not instantly re-set but it did after a couple of minute.

The RCCB supplied: Downstairs power, Upstairs Power, kitchen, Extension, utility/boiler (5mcbs)

So I reset RCCB. Go back to "TV Socket", plug in Martindale socket tester, switch on socket switch and RCCB trips (do this a couple more times and keeps tripping) The TV socket is on Downstairs power MCB.

Homewoner says that its normally the tumble dryer / kettle / microwave (on the utility MCB) that ususally trips the RCCB but once reset they work again.

Reset RCCB and and all MCB's are in the ON position. Go to utility room and plug Martindale socket tester into socket, switch on and RCCB trips again. I try several different sockets and trips every time however when the boiler is fired up it doe not trip the RCCB.

If I turn off the MCB to the Utility room and try my Martindale socket tester in the kitchen sockets then it trips the RCCB. If i turn off the the Extension and utility / boiler MCB then the "TV Socket" does not trip the RCCB and nieither do the kitchen sockets.

Now the extension is actually a 2 storey extension but when I turn this MCB off it only turns the power off to the downstair extension (granted the upstairs may have been taken off the upstairs power)

I took off every socket face on the affected circuits and wiring all looked fine. I checked all cables where possible (ones clipped direct etc) for signs of damage. I asked the homewoner if they have done any DIY recently. I checked all outside equipment for signs of water ingress or damage and everything I checked looked ok and no signs of damage.

The homeowner has lived in the house for approx 4 years and on the face of it it is really modern and had a massive refurb job done by the previous owners but the current homeowner has said they have had quite a lot of problems with te house and especially with the electrics.

I think that there is a dodgy conection somewhere but I couldnt find it so must be burried in / behind a wall somewhere.The junction boxes I found were wired ok. Anyone shed some light on what they think it may be? Ways in which you would try and trace fault? No insulation resistance test was carried out.

There's no gentle way to ask this son, but are you "sure" you know what you're doing there - Martindale Socket Tester an' all?? :uhoh2:
 
Hi Adam ... can you please update or fill out your profile so we know what level you are and then reply accordingly....

Lets assume you are a fully qualified Electrician out on a call with the issue in post 1 unless you correct us otherwise!

You should not go to a job like this and walk without even doing any basic tests, you have come on here asking what could be the problem and you have not followed any of the procedures you were trained to do. Walking away from a job with no idea what the problem is even if you are going back is not very professional, your customer would at least expect a report of your findings which would require testing - not sure what excuse you have used...

Reading throught the post it seems you are unsure of procedures, not fully understanding of earth fault leakage and unfamiliar on how to perform a ramp test.

-Your first step would be to identify the circuit tripping the rcd.
-Your second step would be to ensure all loads are disconnected and test the hardwiring.
-Depending on results of step 2 then either locate detected problem and rectify or reconnect circuit if tested ok and add the loads one at a time been aided by an earth leakage ammeter if you have one or until the device trips again.
-Ramp testing is an additional aid to finding high background leakage or designed earth currents to aid in identifying issues.

Asking how to perform a ramp test on any device is very worrying if you are qualified - your history shows you were in training of your 3rd year in 2012 so are we to assume you now are a practicing Electrician judging by following threads started by you - have you got no mentor or supervisor while you gain experience, yes agree we all have to go through a learning curve but you need to gain at leat 5yrs IMHO under someone elses wing to become a competent Electrician .... I'm hoping you not another one of the straight out of college to self Employment brigade who wing it and rely on forums to answer questions you really should know.

Apologise if I've second guessed your level wrong but we have to do this when you don't fill out your profile and start asking basic questions without even providing any testing data.
 
Here we go with the "I'm bigger and better than you" playground antics. I came here to ask advice / thoughts on what would be the way in which you would have dealt with this. Experience is what is required in this situation but how do I go about getting that? I didn't charge the customer, left them in a better situation then when I walked in the door and explained that they needed someone with the time and experience to deal with their situation.

We crossed posts, but its a shame you didn't explain that you were aware of your lack of experience, and that you had already explained this to the customer.
The advice you have received is not because people are bigger or better.
Its because they know where you will end up.
And for that reason, take the advice as sound and good.
 
Here we go with the "I'm bigger and better than you" playground antics. I came here to ask advice / thoughts on what would be the way in which you would have dealt with this. Experience is what is required in this situation but how do I go about getting that? I didn't charge the customer, left them in a better situation then when I walked in the door and explained that they needed someone with the time and experience to deal with their situation.

I suggest you drop the attitude about the bigger better edge, its clear you have had little or no experience and are trying to form a career by side-stepping a crucial part of the path in working for a firm and using this time to be guided and gain the experience required...
Consider been this customer of yours, regardless of the no charge for your time, the impression you have given him is you are out of your depth and inexperienced. Don't get me wrong this is not a crime or anything to be ashamed of but you need to gain experience with a competent person before you go it alone ..... as is at present you will end up getting a bad name for yourself as customers do talk, chat txt FB and in the modern world its hard to keep a business successful if you keep having to walk away through inexperience.

Find a firm and do 2 - 5yrs to get a grasp of your trade and make sure you have a good mentor and not a company who have little interest in educating you, plus be wary of contract agreements you may be subject to limitations on leaving and setting up again for a few yrs if your target customers is the same as the firm you work for.... this is a normal agreement to protect the business interests of the company who give you that experience.
 
Thank you all for taking the time to reply to me even if some of the posts have got my back up but yes my lack of experience is evident and I take on board the comments.

I haven't come up against a fault like this before and obviously approached it in completely the wrong way. I wasn't using the socket tester to try and show / solve the issue but that has obviously came across in my original post.

Being out off college for sometime now and not working in the industry full time leaves me really nowhere to turn other than forums to pick up advice, wrong doings etc.

The sequence off events that seemed to trip the RCD is what completely baffled me.
Had the fault been local to one circuit, say for instance the utility room circuit, and it was this circuit that was tripping the RCD I would have felt much more comfortable trying to solve it. The fact that every socket on various circuits were tripping the RCD really threw me hence me advising that an better experienced Electrician should take a look.
 
That's why you need someone to cover a methodical fault find procedure isolating all related circuits completely from the board.
Ramp testing the Rcd and IR testing each circuit with no loads connected.
When your experienced sparky arrives try to spend some time with him, you will gain that way a lot more than on a forum.
 
That's why you need someone to cover a methodical fault find procedure isolating all related circuits completely from the board.
Ramp testing the Rcd and IR testing each circuit with no loads connected.
When your experienced sparky arrives try to spend some time with him, you will gain that way a lot more than on a forum.

When fault finding I'd leave loads connected with the exception of highly vunerable equipment like computers.You are looking for a low reading,which is just as likely on connected equipment as on the circuit itself. You want to verify the system as it will be used.As long as you dont do a L-N test...(pointless as far as RCD tripping is concerned)..and if in doubt start with a soft test at 250v there is no risk of damage and more chance of tracing the source of the fault.

To the OP.
RCD tripping is nearly always down to a low IR on either a circuit or connected equipment.Test as above as the first course of action. It constantly amazes me how many of these threads are all about ramp testing etc with no mention of the real cause in 99% of cases....Low IR to earth. Why is it that people seem to assume the RCD is faulty before considering the most likely reason?
I do RCD fault finding with monotonous regularity,and it's rare that I have to get the ramp tester out.....all that is required in nearly all cases is an IR tester. This is backed up by the vast number of times I've attended jobs wher other electricians have replaced 'faulty' RCD's and yet the random tripping continues. If they'd got their IR tester out they'd have found the real cause and saved the client the cost of an unecessary RCD.
 
Last edited by a moderator:
The reason we ask for ramp test or RCD timed test is it is a simple 5 minute that immediatly proves weather it is faulty or not. I know I always test it before anything else as a matter of course.
 
You're both right

I always ramp it too, as said it takes a few moments and can be discounted then.

but also low IR To earth agreed also. Or a knacked up element (same thing, almost)
 
You're both right

I always ramp it too, as said it takes a few moments and can be discounted then.

but also low IR To earth agreed also. Or a knacked up element (same thing, almost)


I have spent the best part of two days searching my copy of "Teach youself to be an electrician in 30 days" but cannot find any trace of that technical term anywhere.
 
I have spent the best part of two days searching my copy of "Teach youself to be an electrician in 30 days" but cannot find any trace of that technical term anywhere.
Fatha man! It's in that book worra writ, ye knaa "Teech asel Sparyin" Selt fower copys niw ye knaa. Me n Yee eesy street next yor man, ye cin fetch wor ma an aal. :)
 
.........The RCCB tripped when the TV was plugged in and socket turned on. RCCB would not instantly re-set but it did after a couple of minute.........


Anyone shed some light on what they think it may be? Ways in which you would try and trace fault? No insulation resistance test was carried out.
You're running yourself around in circles without proper test results. Please take an IR tester, an RCD ramp tester and an earth leakage clamp meter to site and if you still have an issue you can always come back here armed with the test results which will mean people can give you more focused advice and less guesswork.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
RCCB Tripping
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
38
Unsolved
--

Advert

Thread statistics

Created
adam1984,
Last reply from
Marvo,
Replies
38
Views
8,016

Advert

Back
Top