If the supply at source is PME, the 25mm 4 core SWA installation is will not be sufficient as a bonding conductor!! You have a choice, run a separate bonding conductor back to the MET or install a TT system for the whole swimming pool installation. If TN-S your in luck, depending on the Zs values on a 100m of feeder/supply cable!! lol!!
What's the betting no-one provided a connection to the pools re-bar, or to link out from the re-bar to any metallic steps supports, or d/board supports?? lol!! That in it's own, would have given you more than a half decent Ra!!