H

Hawca

I seem to remember in under the 16th Edition, the minimum size RCD at the head was 100ma, this was due to nuisance tripping. Has this been removed under the 17th or am I just struggling to find the regulation for this.
Any help is appreciated.

Thanks
 
Under the 16th fitting a 100mA RCD front end was only necessary on a TT supply and would normally be a time delayed model for discrimination. Such an RCD would not be necessary on a 17th edition installation based on the assumption that all circuits would have 30mA protection in most domestic premises.
 
Putting it simply isn't it down to the run of the tails and material of the CU? i.e. if your tails are buriedand/or you have a metal CU on a TT system you need the RCD?

Or conversely your tails are visible and you have a plastic CU you don't need the "head" RCD.
 
I haven't got my 16th so can't remember if the 100mA is still regarded in the same context as the 17th would.

It was always that the 30mA gave the person protection and the 100mA was for equipment. So for instance if you go to section 705 you will see in reg 705.411.4 that a 100mA RCD is needed for socket outlets rated over 32amp, and I think it was the same for the 16th.

In domestic situations especially TT systems the use of the 100mA RCD was deemed necessary because of the instability of the earthing rod, and therefore the high Zs.

With the advent of the 30mA RCD for socket outlet protection for the use of mobile equipment used outside in the 16th, it was still deemed acceptable to have the lights, cookers, immersion heaters etc covered by the 100mA and therefore have discrimination.

Of course the 17th now requires much more additional protection by 30mA RCD.

As for the Reg concerning the size of an RCd at the head I can't recall a specific one, but as I said I don't have my 16th with me.
 
to give more info, Ive carried out a PIR on a house, 15 years old, wire Red and Black, so we know its under the 16th.

TN-C-S with a 30ma at the head.

do i code this as a 4, or even a 2 as under 16th 100ma was the smallest at the head or leave it?
 
Using a 30mA RCD for up front protection would not comply with Regulation 314.1, in so far as avoiding hazards and minimizing inconvenience in the event of a fault.
You would have to decide whether having all the circuits switch off in the event of a single fault on a single circuit is particuarly hazardous, when deciding which code to apply.
If you though that the risk is negligible, then 4, if however you thought there may be some risk for instance due to all the lights going off when someone tries to use the cooker, or when the compressor on a fridge cuts in. Then 2 might be more appropriate.
 

Reply to RCD at the Head in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
93
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
889
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

If the main DB RCBO is there to provide additional protection (as it most probably is), then no, as S type RCDs are not suitable for providing...
Replies
1
Views
2K
loz2754
L
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top