rcd bust? | on ElectriciansForums
Discuss rcd bust? in the UK Electrical Forum area at ElectriciansForums.net
Coventry
[ElectriciansForums.net] rcd bust?
strange goings-on or it might be me, this is what happens;
• 3 lead loop test on final circuit = rcd trip
• 3 lead loop test at board, outgoing side of rcd, all circuits off = rcd trip
• 3 lead loop test at incoming side = rcd trip
• rcd test at outgoing side= X.5 no trip X1 45ms X5 29ms
•rcd test income side no trip at 500mA
• 2 lead loop test on incoming side = L-N and L-E both ~ .35ohms
why is it tripping on the 3 lead test, especially on the incoming side?
this is a remote board supplied by 16mm 3 c swa.
cheers.
Hi Adie, I've only seen RCD trip from current going through it, so is there possibility of weird wiring? Or reversed leads (sorry - just clutching at straws). I was wondering what prompted you to try the RCD test before the RCD?
Reply to rcd bust? in the UK Electrical Forum area at ElectriciansForums.net
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
6K