Just fitted a cooker as soon as energised RCD triped. All wiring correct etc.
Tenant says had a few problems with intermittent tripping.
Old cooker was gas with ignition plugged into 13A socket fed from old electrical oven circuit 6mm cable. I have utilised this.
Did I/R Test on circuit. Live-neutral >500, Live-Earth >500. Neutral-Earth 1.45m ohms.
Ramped RCD at 33ma
1/2 timer IdeltaN - Trip 0'00ms
Faulty RCD yes.
But faulty circuit aswell? Under 2mohm