As an interested and pondering student, I noticed an "error" today that my tutor is unable to clarify to me. In the big yellow book, table 41.1 shows Maximum disconnection time on a TN system at 230v~ is shown as being 0.4s, yet 415.1.1 states "an operating time not exceeding 40ms."
If my maths recollection is correct, 0.4s is 400ms, not 40. Anyone know why, or it just such a negligible amount no one is bothered.

thanks
 
The maximum disconnection time of 0.4s is the maximum disconnection time required for a final circuit. For a distribution circuit it's 5s.

The 40ms is the maximum operating time for RCDs when being used for additional protection.

Or at least, that's my understanding.

Edit:- In short, it's not an error :)
 
The maximum disconnection time of 0.4s is the maximum disconnection time required for a final circuit. For a distribution circuit it's 5s.

The 40ms is the maximum operating time for RCDs when being used for additional protection.

Or at least, that's my understanding.

Edit:- In short, it's not an error :)

ahhhhhhh
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Grimsby
Business Name
DTR Technical

Thread Information

Title
RCD Disconnection query - pondering
Prefix
N/A
Forum
Electrical Course Trainees Only
Start date
Last reply date
Replies
2

Thread Tags

Advert

Thread statistics

Created
Dave Rudderham,
Last reply from
Dave Rudderham,
Replies
2
Views
94

Advert

Back
Top