the pict

-
Mentor
Joined
Dec 30, 2010
Messages
1,194
Reaction score
292
Location
Brodick
I am doing a couple of board changes some re-wire, and replacing some VIR,However the PIR was not done by me, so I am more or less doing a new PIR and the remedial work as I proceed, I am using the original PIR as a guide also which, although done by a national company is pretty poor in some aspects, one comment I cant quite understand is: on a sub board there is no dicrimination between RCD 1 which supplys/isolates this board and the RCBO,s controlling the circuits contained within this board, the RCD is an 80A and no RCBO is greater than 32A, How would you interperate this, I do not have the folder with me to quote directly, can it be that the 80A RCD is suppling a 100A mainswitch in the sub, cant see it my self, it is not bothering me at all but I just wonder maybe I am missing something obscure.

Pict
 
The 80 amp and 32amp is just the rating of the RCD, same as a 100amp double pole switch is the rating on a main switch. It just means that the appliance is rated at a certain limit.

The discrimination you are referring to is the mA rating, I assume both this 80amp RCD and the RCBOs are both 30mA, and so you have no discrimination on fault protection.
 
what is the discrimination you mean? is it the Amp rating or the mA rating of the RCDs/RCBOs? don't forget that the 80A rating of the RCD is it's rated operating current, not a trip threshold.
 
if both the RCD and RCBOs are both 30mA, then you have no discrimination. if they are in the same location, however, that is not a major problem.
 
Just a thought, as far as I remember which discrimination was not mentioned just the lack of it, so I really dont know, maybe he classed it as an outbuilding ( beer celler out back) and was looking for a 100mA rcd suppyling it as in the 16th ?? solution suggestions
anyone
Pict
 
Still no wiser, both RCD's have absolutly no writing left on them I can just about make out 30mA on one, here's another one not mentioned on the PIR, a 19A fryer fed from a service fuse used in the same way we would use a henly as connection point through a remote RCD 80A 30mA in 15 metres of 16mmT&E ran outside round the building in through the gable end and into a switch disconnector any way made me smile, and wonder where my 20mm masonary drill is, as I will have to go through a couple of walls on this one
Pict
 

Reply to RCD discrimination to a RCO board in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Adding a led strip isn't going to make much difference to the 3 phase balance. No real difference to where a 3 phase machine uses one phase to...
Replies
2
Views
349
  • Question
My thoughts exactly! Snowed under with work at the moment, so might have to pass it on 😬😬
Replies
4
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top