Just found this paragraph in the DTI guidelines?
The PME earth cannot be taken outside the equipotential zone. This is to prevent the potential shock hazard should the supply neutral ever be lost.
Is the source of this the 17th edition somewhere - anybody?
You are not ''Exporting'' anything, you are in fact ''Extending'' the equipotential zone when there are extraneous services/metalwork etc!! Which is why you need a minimum 10mm bonding conductor in such circumstances. If no extraneous metalwork then all you require is the standard CPC....
Have you not read the ''EXPORTING PME'' Sticky thread on this forum?? Perhaps you should, it'll answer most if not all your queries on this topic....