I am trying to design a wiring layout for an outbuilding which will be fed from the main house supply.
The main house supply is protected by a fairly old (20yr) Crabtree 100A RCCB with a 30 ma trip. (No time info marked on the unit but is to BS 4293)
I want to protect the outbuilding with a single RCD which will trip out 1st and not affect the RCCB at the main house. Any ideas on how I can achieve discrimination with the existing RCCB or will I need to replace it with something more modern/suitable.
 
AFAIK the only way to guarantee rcd discrimination is for one to be a time delay which wouldn't be suitable in this case. Having different IΔn values isn't certain to work. Best is to have the distribution cable coming from an unprotected way.
 
suggest you take your supply from the incoming side of your house CU (Henley Block the tails) come off in SWA then the outbuilding doesn't affect the house installation in case of a fault. You can earth the SWA at the house end, and use that for your earth or TT the outbuilding
 

Reply to RCD discrimination in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
350
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
898
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
955
He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
626

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top