D

Daniel Son

hi guys im an apprentice and need some more understanding about rcds
please may i have an example of rcd discrimination and what ratings i would use for different things and why
thanks danny
 
RCD Discrimination:
The old "Rule of Thumb" (RoT) was that the upstream RCD nominal trip rating should be at least 3 times larger than the downstream RCD.
Although this often provides discrimination it is not guaranteed. It was the RoT that was universally used by Sparks at a time when, although time delay RCDs where in manufacturers catalogues, they were expensive and only available by special order, so were rarely used and then usually only in industrial installations.
From the 16th Edition of the Wiring Regulations time delay (S type) RCDs have become increasingly common in domestic installations and today their wider usage has reduced the price close to parity with normal RCDs.
The current Rule of Thumb is:- The upstream RCD should be a time delay (S type) RCD and it's nominal trip rating should be at least 3 times larger than the downstream normal type RCD.
 
Last edited by a moderator:
RCD Discrimination:
The old "Rule of Thumb" (RoT) was that the downstream RCD nominal trip rating should be 3 times larger than the upstream RCD. Although this often provides discrimination it is not guaranteed. It was the RoT that was universally used by Sparks at a time when, although time delay RCDs where in manufacturers catalogues, they were expensive and only available by special order from the manufacturer, so were rarely used and usually only in industrial installations. From the 16th Edition of the Wiring Regulations time delay (S type) RCDs have become increasingly common in domestic installations and today their wider usage has reduced the price close to parity with normal RCDs.
The current Rule of Thumb is the downstream device should be a time delay (S type) RCD and it's nominal trip rating should be 3 times larger than the upstream normal type RCD.

what rcd ratings should i use and were?
 
Markie, unless I need another coffee, isn't that UP & DOWN stream the wrong way around?
 
Oops! sorry guys ... I rushed it and didn't proof read it before posting ... now edited. Thanks for the heads-up, nice that you guys were on the ball.

A common example Daniel, Upstream device 100mA S type RCD ... downstream device 30mA RCD.
 
Last edited by a moderator:

Reply to rcd discrimination in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
865

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
949
  • Question
Protection from what? What kind of problem with the inverter is going to be helped by having an RCD on the circuit?
Replies
5
Views
2K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top