Has any one else had this, just installed a dual split board,

Make wylex, when testing both RCD units it failed the first test which is the half rated test or non trip test.

Now I did the test away from the board and at the board but made no difference!

has this happened to any one else please advise..

My test gear is megger and it less than six months old and its used alot...:smiley2:
 
Does sound like a faulty batch. Did you ramp them to see what they are tripping at.

If you tested just at the socket I would also have thrown in perhaps you a load still connected somewhere, which will affect results, but you say you also tested at the CU ...................you did of course isolate the MCBs when you tested at the CU ?
 
Monkee - might sound a daft question, but how are they failing - is it that they are not tripping? ( there not supposed to!). i used to use quite a few Wylex boards, and only ever had a couple with problems, and that was the x5 tests on both
 
This will work for faulty Wylex RCD's that trip upon energizing aswell... Turn all the power off by the main switch and then give the front of the RCD (where the 'WYlex 80A 30mA RCD' is wrote or whatever it is) a good couple of hits with either ur fist or the handle of your snips. Power it all back up and it should of cured it.
 
This will work for faulty Wylex RCD's that trip upon energizing aswell... Turn all the power off by the main switch and then give the front of the RCD (where the 'WYlex 80A 30mA RCD' is wrote or whatever it is) a good couple of hits with either ur fist or the handle of your snips. Power it all back up and it should of cured it.
Does the owner need to do this if her dear hubby is getting a shock off his lawn mower just to make sure it operates correctly when needed, if this is how to solve the problem then their is an inherit design flaw and tech' should be talked to to try find an acceptable solution.
 
This will work for faulty Wylex RCD's that trip upon energizing aswell... Turn all the power off by the main switch and then give the front of the RCD (where the 'WYlex 80A 30mA RCD' is wrote or whatever it is) a good couple of hits with either ur fist or the handle of your snips. Power it all back up and it should of cured it.

If all else fails “HIT IT”

I just hope you write in jest!
 
If all else fails “HIT IT”

I just hope you write in jest!

Not neccesarily, my dads solution to most problems like this is to reach for the hammer, i have since removed all hammers from his house, the only time i use one for non hammer work is when the vending machine does not give me my change.
 
If all else fails “HIT IT”

I just hope you write in jest!

Tis tha Yorkshire way, lad.

I came home once and the barstewards had broken in and put a card meter in, for some reason I lost the plot and smashed it up with a hammer (I'm not a violent man at all, honest (also from Leeds))
Reported it and they came round and replaced it, no questions asked.
 
Let me clear this up, when it happened whilst we were on the council rewires in leeds we phoned wylex and from what i remember they said that after they are made and stored flat in the fuseboard something inside it sticks and it needs a tap to release it when its installed. Obviously you check the functionality and test the RCD when testing. If it's still faulty, not tripping, not tripping in time, or tripping on half times you replace it. When i said hit it, i didnt mean hit it hard like your chopping out on red brick.
 

Reply to Rcd fail half test wylex in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
723

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top