Hi guys, Got a bit of a problem with an RCD fault that cant get my head round!!!

Just done a board change and there were two pyros in one mcb that now trip rcd when turned on. Cant find any dead short on either cable and can only find one of them leading to a socket outlet.

Board is a sub main and is on rcd main switch so no possible neutral mix up!!?!!

Any ideas?
 
Try a 1000v IR test if the usual 500v one is inconclusive...I,ve known that show up a fault when a 500v test was clear on pyro's.
Edit...make sure there's not a computer on the other end though:eek:
 
Last edited by a moderator:
Did you have to re-pot them???

Were they bent back and fore a lot when you re-terminated them into the new CU???

Have you definately got correct polarity???

Sounds like an L-E fault for sure.
 
Didnt have time to delv into it today and left board isolated. Will look into it again tomorrow.Haven't re-potted them so could be that. Also just remembered that the sub main was quite strange. Wired in singles through conduit the live conductor was 4mm Neutral 6mm with an earth of 1.5mm being fed from a 32a mcb. Was thinking to pick it up on the test that new feed should be installed or at least a bigger earth!!
 

Reply to RCD Fault in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

Similar threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
856
  • Question
I misread it.
    • Like
Replies
13
Views
926

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top