Joined
Mar 2, 2019
Messages
27
Reaction score
4
Location
London
Hello, I’ve just been to a job and their RCD has it’s moments and trips throughout the day but doesn’t on other days. When I was there I tested all appliances and put everything on but couldn’t get it to trip. Very weird.
I noticed the test button on the RCD wasn’t working AND was getting slight continuity between incoming live and neutral through the RCD in my two prong megger continuity testers. I’ve changed the RCD for a new ones as I thought it would be faulty. New one is okay and all circuits not tripping it.
Anyone come across this before or any advice if it isn’t a faulty RCD?

I’ve told the customer to contact me if it continues tripping.
 
Hello, I’ve just been to a job and their RCD has it’s moments and trips throughout the day but doesn’t on other days. When I was there I tested all appliances and put everything on but couldn’t get it to trip. Very weird.
Anyone come across this before or any advice if it isn’t a faulty RCD?
It can be quite common and you could almost say 'it could be anything'. It's a case of testing and process of elimination. An earth leakage test instrument could prove to be handy.
 
slight continuity between incoming live and neutral through the RCD

Can you put that in ohms? It's odd, nearly impossible without the RCD blowing up, and deserves explanation. Was the RCD completely disconnected from the outside world when you made this test?
 
Can you put that in ohms? It's odd, nearly impossible without the RCD blowing up, and deserves explanation. Was the RCD completely disconnected from the outside world when you made this test?
Everything disconnected. Continuity Testers were bleeping and flashing super fast as if a connection was being made then broken really quickly. I’m thinking it’s just the RCD being faulty and creating some kind of weak connection inside. Either that or my testers are playing up
 

Reply to RCD FAULT in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
957
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
693
Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
499

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top