eskimo39
Evening All, have been to a customers house this evening who is having a problem with her RCD not staying in causing her to be sat with no power all day. When I got there I stripped down the full board and removed all L,N & E conductors from breakers and bars leaving the board in a 'as new' condition. Even with nothing attached the RCD would still not stay in everytime and the few times I got it to stay in to do a ramp test on, it would trip before my fluke even registered any current (0.00mA).
This lead me to believe it is the RCD at fault so I will be replacing that tomorrow. I have installed a small 2 way RCD board which I usually use to put temporary power on building sites and just given her lighting & sockets to get her through tonight. However this even tripped once so I am now thinking there is also a fault on one of these circuits as well????
Does anyone know if I buy a cheap Earth Leakage Clamp meter tomorrow : Dilog DL6507 10uA to 60A AC Leakage Clamp meter. Buy online or call is it as simple of being able to clamp it on the main earth of the installation and take a reading, then re connect each circuit one at a time whilst monitoring the earth leackage shown on the meter until I find one with a noticable increase.
If nothing shows an increase in earth leackage I would then plan on keeping someone monitoring the clamp meter whilst going around the house switching on appliances/lights etc until a noticable rise in leakage shows on the meter.
If then that still shows no increase I would then assume the fault would most likely be on a compressor or something timed, so I would have to go down the awful route of disconnecting appliances etc for periods of time to see if we could solve the fault.
Is this how others would go try to solve this or do you have any other advice you can give. Also does anyone own an earth leakage meter they can recommend???
Cheers
This lead me to believe it is the RCD at fault so I will be replacing that tomorrow. I have installed a small 2 way RCD board which I usually use to put temporary power on building sites and just given her lighting & sockets to get her through tonight. However this even tripped once so I am now thinking there is also a fault on one of these circuits as well????
Does anyone know if I buy a cheap Earth Leakage Clamp meter tomorrow : Dilog DL6507 10uA to 60A AC Leakage Clamp meter. Buy online or call is it as simple of being able to clamp it on the main earth of the installation and take a reading, then re connect each circuit one at a time whilst monitoring the earth leackage shown on the meter until I find one with a noticable increase.
If nothing shows an increase in earth leackage I would then plan on keeping someone monitoring the clamp meter whilst going around the house switching on appliances/lights etc until a noticable rise in leakage shows on the meter.
If then that still shows no increase I would then assume the fault would most likely be on a compressor or something timed, so I would have to go down the awful route of disconnecting appliances etc for periods of time to see if we could solve the fault.
Is this how others would go try to solve this or do you have any other advice you can give. Also does anyone own an earth leakage meter they can recommend???
Cheers