Hi all
Been to a house today to carry out a PIR mem split load board 100amp ms / 30ma rcd on a tt system , when carrying out no trip earth loops the rcd trips. I ramp tested the rcd and its tripping in 18ms, anyway i bridged out the rcd all e loops are fine. however the client would like a shed supply installed obviously on the rcd side would this be a faulty rcd ? hence tripping on e loop ?
If so i have to change the board as the trip is now discontinued
Been to a house today to carry out a PIR mem split load board 100amp ms / 30ma rcd on a tt system , when carrying out no trip earth loops the rcd trips. I ramp tested the rcd and its tripping in 18ms, anyway i bridged out the rcd all e loops are fine. however the client would like a shed supply installed obviously on the rcd side would this be a faulty rcd ? hence tripping on e loop ?