Hi all

Been to a house today to carry out a PIR mem split load board 100amp ms / 30ma rcd on a tt system , when carrying out no trip earth loops the rcd trips. I ramp tested the rcd and its tripping in 18ms, anyway i bridged out the rcd all e loops are fine. however the client would like a shed supply installed obviously on the rcd side would this be a faulty rcd ? hence tripping on e loop ?

If so i have to change the board as the trip is now discontinued :mad:
 
What meter are you using? I know there are problems with some Megger 1700 range tripping on the no trip setting.
 
test the RCDvfor trip times at x1 and x5. if within limits, ( 200mS) then OK.
 
Last edited:
If it's a 30mA RCD it has to not trip at half the current ie 15mA for a period of 2 seconds. if it doesn't trip then it is not a failure. I suspect it won't trip. It passes by the skin of it's teeth!!
 

Reply to Rcd faulty ? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
312
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
834
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
941

Similar threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
862
I would probably C3 it, based on no contact with sharp edges, all the terminations being tight, and no signs of any thermal damage. With all...
Replies
2
Views
964

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top