When does an installation NEED an RCD? I thought that all new circuits need one but I now believe that I am mistaken.

Regulation 411.3.3 for socket outlets up to 32amps and regulation 411.3.4 for lights.
Then for special locations like bathrooms.
If the cables are less than 50mm deep into the wall

So when I'm installing a new oven, boiler or any fixed equipment really I don't technically need an RCD protecting the circuit? Unless ofcourse the manafacturer's instruction say so.

thanks
 
As you have said RCDs are required for specific things only, there is no blanket requirement for RCDs on all circuits.

In practice the vast majority of new final circuits in a domestic installation will need RCD protection due to cables being buried at less than 50mm etc, serving a bathroom, serving lighting circuits or being the easiest way to RCD protect the sockets.
 
If doing a like for like swap then you wouldn't technically need to install an RCD however it would always be advisable to recommend to the customer that one is installed if required.
 
How many boilers have thier own feed? I suspect most are just taken from a FCU off the nearby ring and get whatever it has! (Which these days ought to be RCD protected)
 

Reply to RCD for boiler replacement? When is an RCD NEEDED? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
159
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
526
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
474

Similar threads

All socket outlets up to and including 32A (which are commercial, not domestic) are required to be 30mA RCD protected. By the sounds of it you...
Replies
5
Views
1K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
933

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top