Query regarding a Passive RCD fused spur unit protecting a bank of 4 led downlights supplied via switched live and nuetral. I have been asked to replace the downlights. Cant be totally sure but i think RCD spur was to protect the (addition)of the downlights. The rcd is passive so will remain latched when switched.
 
Sounds like a bit of an odd arrangement but there is no particular reason to change it if you were changing the downlights.

The lights would not require 30mA RCD protection; unless they are in a bathroom in which case the circuit feeding the bathroom would need protection.
If the cable is buried less than 50mm in a wall then that would need to 30mA RCD but presumably the cable before the switch would also be needing RCD protection so the addition seems odd.
I can see that if the cable were surface run and it was a switch fed wiring arrangement going to bathroom downlights then a 30mA RCD after the switch would be a compliant method of installing the downlights, but not generally the way I would do it.
 
Query regarding a Passive RCD fused spur unit protecting a bank of 4 led downlights supplied via switched live and nuetral. I have been asked to replace the downlights. Cant be totally sure but i think RCD spur was to protect the (addition)of the downlights. The rcd is passive so will remain latched when switched.
Passive rcd?
 
A passive rcd spur stays latched on in the event of voltage loss/power cut. The other type non passive or active switch off with voltage loss/power cut bit like a no-volt release.
Well thanks mate, learning never stops does it, have seen that type but by a different name, don't ask me what name it was a while ago and my memory isn't what it was/should be
 
Sounds like a bit of an odd arrangement but there is no particular reason to change it if you were changing the downlights.

The lights would not require 30mA RCD protection; unless they are in a bathroom in which case the circuit feeding the bathroom would need protection.
If the cable is buried less than 50mm in a wall then that would need to 30mA RCD but presumably the cable before the switch would also be needing RCD protection so the addition seems odd.
I can see that if the cable were surface run and it was a switch fed wiring arrangement going to bathroom downlights then a 30mA RCD after the switch would be a compliant method of installing the downlights, but not generally the way I would do it.
The downlights are in a toilet cloakroom.(Bungalowe) No cables buried less than 50mm all are located in loft void. Switch is a ceiling pull switch, so all cables are surface. I agree Richard an odd arrangement and not the way i would usually do it.
 
Im assuming that the Powerbreaker RCD Fused spur which is passive will operate correctly even though its supply is being switched via the pull cord light switch. Ive looked on the green brook website no information available
 
Im assuming that the Powerbreaker RCD Fused spur which is passive will operate correctly even though its supply is being switched via the pull cord light switch. Ive looked on the green brook website no information available
Don't see why not but obviously will only function when the lights are on.
 
Im assuming that the Powerbreaker RCD Fused spur which is passive will operate correctly even though its supply is being switched via the pull cord light switch. Ive looked on the green brook website no information available
Ditto above, but I'm not sure if the constant powering up & down of the rcd is going to do it any good? If the rcd is not required, why not remove it?
 

Reply to RCD fused spur in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
355
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
908
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

J
The rcd spur being fitted is probably because there wasn't rcd protection of that supply.
Replies
5
Views
439
hI Gent's. I I can explain this spur line briefly, maybe someone can help me? Everything is Spur, no rings. Inside of the house and main fuse...
Replies
0
Views
326

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top