Farm job im at has a problem


three phase tt system comes into main barn area, three phase main distribution board (with 100mA s type 4 pole rcd as main switch) supplying barns and general farm buildings

Swa single phase supply to farm house(around 40meters away), supplied directly from meter side of distribution board on henly blocks to switchfuse/rcd

so house supply is totally independent from the barn supply

however everytime there is a fault on the barn distribution board and its main rcd operates it takes out the rcd at the farm house too

i havent been over to the farmhouse yet but i cant understand why it would be knocking out the rcd in the house?

any ideas?
 
Where abouts is the suppliers transformer ...is it close up a pole?
What kind of rcd's are they - are they modern type that measure inbalance between L/N?

Have you ensured all your customer side connections are sound and tight... check busbar tabs are on the correct side of any mcb, rcd and main switch terminal clamps.
 
If theres a single earth stake in use for both barn and house , and all bonding is done at the house , it could be the Ze of the earth stake is higher resistance than the bonding at the house and fault currents are back fed to house , just a thought,,
 
This reads plain to me but a few are not reading the OP properly ...

At mains there is a 3ph board with 100mA rcd main switch
Also a 1 phase supply straight of the meter via a henley block to a sw/f + RCD ...lets assume 100mA

When a fault trips the rcd of the 3ph board the rcd IN THE house trips so assuming a 30mA is tripping in the house possibly 17th edition board.... can the OP confirm this!?


Edit confirmed in post 15.
 

Reply to Rcd head scratcher in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top