Farm job im at has a problem


three phase tt system comes into main barn area, three phase main distribution board (with 100mA s type 4 pole rcd as main switch) supplying barns and general farm buildings

Swa single phase supply to farm house(around 40meters away), supplied directly from meter side of distribution board on henly blocks to switchfuse/rcd

so house supply is totally independent from the barn supply

however everytime there is a fault on the barn distribution board and its main rcd operates it takes out the rcd at the farm house too

i havent been over to the farmhouse yet but i cant understand why it would be knocking out the rcd in the house?

any ideas?
 
This reads plain to me but a few are not reading the OP properly ...

At mains there is a 3ph board with 100mA rcd main switch
Also a 1 phase supply straight of the meter via a henley block to a sw/f + RCD ...lets assume 100mA

When a fault trips the rcd of the 3ph board the rcd IN THE house trips so assuming a 30mA is tripping in the house possibly 17th edition board....






can the OP confirm this!?






Thats how I read it as well ...
 
I thought I had read it right, what I thought was, "what is protecting the single phase supply"? it is from henley blocks to a switch fuse then to the house where there is a rcd?? or does he mean there is a rcd in the barn at the supply, oh dear I am now getting confused too
 
Where abouts is the suppliers transformer ...is it close up a pole?
What kind of rcd's are they - are they modern type that measure inbalance between L/N?

Have you ensured all your customer side connections are sound and tight... check busbar tabs are on the correct side of any mcb, rcd and main switch terminal clamps.

rcds/mcbs are mem old 3871/4293 type, dunno about house end ive not been able to get access in there yet but assuming they are of similiar age

also not sure of tx location
 
This reads plain to me but a few are not reading the OP properly ...

At mains there is a 3ph board with 100mA rcd main switch
Also a 1 phase supply straight of the meter via a henley block to a sw/f + RCD ...lets assume 100mA

When a fault trips the rcd of the 3ph board the rcd IN THE house trips so assuming a 30mA is tripping in the house possibly 17th edition board.... can the OP confirm this!?


Edit confirmed in post 15.


Spot on darkwood yes 100mA s type sp protecting submain(this is holding fine but the 30ma rcd in house is tripping out with the 3pn board in the barn)
 
well certainely a headscratcher alright, seems very strange, maybe the fact both supplys connect to the rod and the fact a surge to earth trips the one may mean the other is over sensitive, must admit it is a funny situation which I am struggling with at the moment.
 
La de da da da ....any chance of responding to post 2 yet its getting further away as we speak... might be using the 18th edition by the time you respond to it :juggle2:

Please refer to post 21 for guidance.
 
Welchyboy1 however everytime there is a fault on the barn distribution board and its main rcd operates it takes out the rcd at the farm house too any ideas?[/QUOTE said:
A strange one indeed .

first thing to do would be confirm this is actually happening with test meter .

you know how customers can somehow get the wrong end of the stick .
 
well certainely a headscratcher alright, seems very strange, maybe the fact both supplys connect to the rod and the fact a surge to earth trips the one may mean the other is over sensitive, must admit it is a funny situation which I am struggling with at the moment.


It is a pain

im thinking of isolating the two earthing systems from each other, having a rod for each and insulating the SWA sheath at the house end from the barn see what happens

just wanted a few ideas for when i get back there

Ramp test the house RCD
 

Reply to Rcd head scratcher in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top