Just wondering if anyone has come across this before,

we got called to a intermittent fault at a new build the owners have been moved in around 8 months, the power would
trip mainly when all the lights were switch on and in the evening when switches were turned on, but sometimes
randomly, I tested the rcd first and would test fine when lights were disconnected but not always when connected,
also when you turn off the main switch both RCDs would trip most of the time and when boiler is turned off.

Thanks
 
Test the RCD with no loads connected. If these tests are good then the fault is on the circuits. It could be accumulative leakage or an intermittent fault which could be verified by additional testing.
 
Would come up with trp on x1/2 but would test x1/2,x1 and would trp at x5 with some of the lights disconnected, I have a megger MFT1553, also have installed new RCDs

Cheers
 
As Sintra suggests, ramp test the RCD with no load connected. If it passes then start looking for the leakage faults on the circuits themselves.
 
Thanks for the replys, RCDs are fine on ramp test and without load, on the circuits what could be the main causes there are a lot of LED Downlights and the problem has just started?

cheers
 
Last edited by a moderator:
If the LED downlights have their own driver units there could be standing leakage from the internal surge arrestors. Use an earth leakage clamp around both the L+N simultaneously and switch the lights on to establish the leakage. If it's just an accumulation of many devices adding up to the 30mA threshold then you may need to reconfigure and put the circuits on RCBO's.
 
If the LED downlights have their own driver units there could be standing leakage from the internal surge arrestors. Use an earth leakage clamp around both the L+N simultaneously and switch the lights on to establish the leakage. If it's just an accumulation of many devices adding up to the 30mA threshold then you may need to reconfigure and put the circuits on RCBO's.

thanks Marvo
 
I can't see how an electrician can get by without a leakage clamp these day's to locate earth faults and RCD tripping issues , especially on dual RCD CU's. But then you need to know how to use them and interpret the values being shown!!
 

Reply to RCD intermittent fault in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
701
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
735
Update. Went back today as it was popping the other RCD post move, again intermittently with no real pattern. Typically overnight but not every...
Replies
6
Views
274

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top