Hi All
I have just done a board change at a house that i'm sure is a TT System. (The House is supplied by overhead cable to the house with an earth rod net to where the external meter is fitted).
Once I had changed the board, I did a ZE Reading and GOt 5.63 Ohms. When testing the 30mA RCDs on the board it was tripping on half limit.
Has anyone experienced this with a TT System??
Had an RCD go down on a customer this morning. One ring final circuit with every thing on it kitchen, front room, hallway and backroom. I split the circuit in two and found the fault in the kitchen. Line to earth fault which took 3 hrs to find.
Reply to RCD Issue, Tripping at half Limit... in the UK Electrical Forum area at ElectriciansForums.net
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.