ample current
hello every body,
I have been to a house this evening after a customer calls regarding a tripping rcd, I did the usual, all circuits off then on 1 by 1, it seems to randomly trip regardless of which breaker is switched back on, even mcbs on the non rcd side caused it to trip, which I thought a odd. Ramp test proved the rcd faulty, wouldn't trip when 33mA were reached, normal I delta n woudnt trip in 300mS. The board was a slit load vynckier installed when the house was bit probably mid 80's, so I doubt much chance in finding a replacement rcd.
the thing that got me the most was the fact circuits not connected through it tripped it???
Would the fact the rcd was not functioning properly (as in not tripping when tested) cause it to trip for no apparent reason like switching the oven on (oven no connected through rcd)
I have been to a house this evening after a customer calls regarding a tripping rcd, I did the usual, all circuits off then on 1 by 1, it seems to randomly trip regardless of which breaker is switched back on, even mcbs on the non rcd side caused it to trip, which I thought a odd. Ramp test proved the rcd faulty, wouldn't trip when 33mA were reached, normal I delta n woudnt trip in 300mS. The board was a slit load vynckier installed when the house was bit probably mid 80's, so I doubt much chance in finding a replacement rcd.