A

ample current

hello every body,

I have been to a house this evening after a customer calls regarding a tripping rcd, I did the usual, all circuits off then on 1 by 1, it seems to randomly trip regardless of which breaker is switched back on, even mcbs on the non rcd side caused it to trip, which I thought a odd. Ramp test proved the rcd faulty, wouldn't trip when 33mA were reached, normal I delta n woudnt trip in 300mS. The board was a slit load vynckier installed when the house was bit probably mid 80's, so I doubt much chance in finding a replacement rcd.
the thing that got me the most was the fact circuits not connected through it tripped it???
Would the fact the rcd was not functioning properly (as in not tripping when tested) cause it to trip for no apparent reason like switching the oven on (oven no connected through rcd)
 
Did you ramp test the RCD with the loads disconnected? Also did you carry out any IR tests?

Getting the RCD to stay on with any load connected to the rcd or not was near impossible, what difference would that make anyway. IR between line and E were ok. Customer has decided on an new CU after finding a couple of other faults so will be carrying more comprehensive tests then.
 
Getting the RCD to stay on with any load connected to the rcd or not was near impossible, what difference would that make anyway. IR between line and E were ok. Customer has decided on an new CU after finding a couple of other faults so will be carrying more comprehensive tests then.
As Tel suggested probably a N-E fault, have you tested IR N-E? if so what were the results?
 
sorry for late reply, have been way, ok, no neutral earth fault, I did however find 3 socket outlets wired up with neutral live reversed, one in the kitchen possibly done by the kitchen fitter some years earlier but the other 2 were done when the house was originally built 25+ years ago, there were also couple of surge protector leads that were faulty, however these were unplugged when I initially looked for the cause of the tripping.
 

Reply to rcd issue in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
372
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
349

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top