RCD keeps tripping | on ElectriciansForums
Discuss RCD keeps tripping in the Australia area at ElectriciansForums.net
J
JakeC
Hi, I'm new the forum seeking some advice :)
My parents have just had their rewireable fuse board updated and some spotlights installed on the landing.
The problem is the RCD keeps tripping out (only sometimes) when the landing lights are switched on. Now I know you will be thinking borrowed neutral but I've checked the 2 way switch and the cable is 3 core and earth from the downstairs to the upstairs switch...
The upstairs and downstairs have been put on the same RCD also to double check this..
Now in one of the bedrooms the light has 4 bulbs and one has been blown for awhile. I put a new bulb in today and when the bedroom light is on, if you turn the landing light on it trips everytime.. Take 2 bulbs out and it doesn't.
The bedroom bulbs are 4x 25watt and the landing light bulbs are 3x 50watt.
The RCD is 63amp 30mA.
Any suggestions would be appreciated.
Thanks.
Thanks.
Welcome to the forum.
Lovely (I hope that's the before picture :))! If it's not a fault at that fitting then you could check the others on the route back to the CU, with the circuit isolated. I'm assuming that the extra load of another two lights in that bedroom is enough to exceed the threashold.
If it was me I'd be getting the "electrician" back to sort it out.
It's usually a good idea on a two rcd board to have upstairs lights and downstairs sockets on one rcd and downstairs lights and upstairs sockets on the other. In the event of an RCD tripping you can still utilise the sockets for a lamp, either upstairs or downstairs.
The picture is the ceiling rose of the bedroom, been like that for donkeys years lol.
What i mean by the downlights not being earthed. They are chained in 2 core flex with no place to even fit an earth (I pulled one out)
Correct me if i'm wrong but spotlights aren't earthed?
either mains class 1s which require a cpc..or selv..seperated extra low voltage: no cpc on the secondary side...or felv: functional extra low voltage usually requires a functional earth to operate...such as some RCDs, RCBOs...BT etc........
as further to this i shoukd add that an RCD requires an earth path to opperate...
Reply to RCD keeps tripping in the Australia area at ElectriciansForums.net