had a call out today where the RCD would not hold, at first i hadall the MCB's off and ramp tested the RCD and it was tripping at 12-13 mA consecutively.
i've briefly tested all the circuits and theres no earth fault, i've had a clamp meter on the earth and switched on all MCB's individually and then without warning it will just trip, generally as more load was put on. Ie i could put on boiler(combi), cooker (turned off) and up & down lights and it was fine, even with 1 ring on it was fine but as soon as both rings were on it would trip. then sometimes it would hold for 30-40 seconds and trip. also another point to note if i tapped the RCD main switch it would trip. now i don't think thats normal? it's a wylex btw. i have just got home and i have been giving all my square d rcd a good tapping and none of them go??
right then bear with me, all of a sudden i did a full rcd test and it was fine, rcd tripped promptly at x1 and x5, never tripped at x1/2 and ramp test showed 27 and 28 ish mA. the i flicked on all the breakers and it held, and then i got them to boil the kettle and had the clamp meter on live and it was pulling 14A no problem:crazy:
i left them my card and said if it does it again it's likely to be the RCD MS and i'll change it on monday or them.
i hate faults like this, if it had been a private job i wouldn't have taken any money off them as it could go as soon as i walk out the door and then i'd look stupid! it was for a letting agency so i'll invoice them directly on monday if it's still ok, or if it's gone again i'll change the RCD.
oh and something else that might be of relavence, the street was without power the day before, and the problem first occured after that so is it a possilbility that some works by the DNO could have damaged the RCD main switch?
i've briefly tested all the circuits and theres no earth fault, i've had a clamp meter on the earth and switched on all MCB's individually and then without warning it will just trip, generally as more load was put on. Ie i could put on boiler(combi), cooker (turned off) and up & down lights and it was fine, even with 1 ring on it was fine but as soon as both rings were on it would trip. then sometimes it would hold for 30-40 seconds and trip. also another point to note if i tapped the RCD main switch it would trip. now i don't think thats normal? it's a wylex btw. i have just got home and i have been giving all my square d rcd a good tapping and none of them go??
right then bear with me, all of a sudden i did a full rcd test and it was fine, rcd tripped promptly at x1 and x5, never tripped at x1/2 and ramp test showed 27 and 28 ish mA. the i flicked on all the breakers and it held, and then i got them to boil the kettle and had the clamp meter on live and it was pulling 14A no problem:crazy:
i left them my card and said if it does it again it's likely to be the RCD MS and i'll change it on monday or them.
i hate faults like this, if it had been a private job i wouldn't have taken any money off them as it could go as soon as i walk out the door and then i'd look stupid! it was for a letting agency so i'll invoice them directly on monday if it's still ok, or if it's gone again i'll change the RCD.
oh and something else that might be of relavence, the street was without power the day before, and the problem first occured after that so is it a possilbility that some works by the DNO could have damaged the RCD main switch?