Rcd, an imbalance of the live + neutral of the rcd
It could be a live-earth fault or a neutral-earth fault ( it takes little fault current to trip it out)

If you want extreme circumstances for the word "blow" to be approporiate
A dead short of the live and neutral of the outgoing of the rcd,
[ElectriciansForums.net] RCD/mcb





MCB Will operate when the circuit design current is exceeded for a long period or
When a short circuit( live-neutral) occurs to the circuit protected by the mcb
When a live- earth fault causes a whack of fault current to flow
 
so Des ,a RCD that has operated is a voltage fault on one of the circuits its covering ,and a mcb that has operated is a over current fault

As spinlondon answered "leakage" an rcd operates when there is leakage to earth from the balanced live-neutral,either live-earth or neutral-earth

T
 
An rcd moniters current on the outgoing live and the incoming neutral. if earth currents occur , the current on the outgoing live and the incoming neutral will differ . eg . 4A out on live - 1 amp down earth - 3 amp down neutral = imbalance. ie. earth leakage.

In reality the rcd operates when the difference is more than 30mA . ( i think ) .

An MCB works on the same principle as a fuse. When the current exceeds the safe capabilities of the cable . The MCB trips. Such as a short ( no load : high currents ) .

i think ...... :-D
 
The thing about these devices, is that they will both operate when there is no fault.
MCBs provide overcurrent protection. That overcurrent could be caused by a fault such as Line to neutral or Line to earth, or it could be caused because too many high power appliances are plugged into a socket circuit.
RCDs detect earth leakage. This could be caused by a fault between a live conductor and earth, or could occur in the normal operation of an appliance.
 
Just a note on summat i learned recently , ever had the rdc trip when the mcb is off ? ( ie touching the n + e together ?)

Learned that small voltages on the neutral bar creates currents in the earth . and rdc trips.

Baffled me for ages that. lol
 
Just a note on summat i learned recently , ever had the rdc trip when the mcb is off ? ( ie touching the n + e together ?)

Learned that small voltages on the neutral bar creates currents in the earth . and rdc trips.

Baffled me for ages that. lol

First time it happened to me I thought the house was haunted, lol.

The neutrals are connected together at the CU. So even though you have locked off the CB on the circuit you're working on, if you short the neutral to earth while working on it,it gives an alternative path for the current flowing in the neutrals of the other circuits. That causes the RCD to trip.
 

Reply to RCD/mcb in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
487
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
962
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
901

Similar threads

Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
936
  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
610

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top