Hi,
I'm investigating an intermittent problem in a flat. Every once in a while the RCD trips. The tenants have narrowed it down to one circuit, the electric hob. However, it never trips whilst I'm there, even after pouring water on the hob. I've carried out 500v insulation resistance tests, and all OK. I then carried out a ramp test and the RCD trips at 21mA. Is this too sensitive?
The RCD did trip once whilst I was there, but wouldn't trip again.
 
intermittent fault on one of the elements when warm. only way is to track it down by trial and error. turn 1 element on at a time till you find the 1 that trips the RCD. 21mA is not bad. there could be a small leakage elsewhere.
 
Black iron heating elements absorbe moisture which can cause earth leakage.
You will also find leakage to earth when the elements are on their way out.
I would switch on each element and look for bright spots which would indicate wher a fault is developing.
If there is no bright spot, then it is most likely just moisture absorbtion.
 
Do you have a earth leakage clamp meter to see how much its leaking could be if you only have 1 RCD on the CU its the total amount thats sometime putting it over the 21 mA with other appliances switched on.

These faults can be time consuming and frustrating to say the least maybe a RCBO on that circuit if possible to minimise inconveniance!
 

Reply to RCD minimum times... in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

  • Question
Just an update for anyone interested, I got another rod in outside today, which has lowered the Zs db to a more healthy 53ohms. The oven elements...
2
Replies
19
Views
3K
I fitted a Mem MR30 Pod and MCB, about ÂŁ75 for both.
Replies
8
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top