Greetings.
I am an electrician wannabee and am doing a spot of labouring for an electrician. Maybe not a wise career move at this time but it's too late to change now.
My electrician boss and I were having a discussion about why an RCD would trip even if all the MCBS connected to it were switched off and he said it was caused by an earth neutral fault.
I asked how can there be an earth neutral fault when all the circuits supplied by that RCD were switched off and hence no power was going through the RCD. He didn't know the answer and neither do I.
I was wondering if anyone could shed some light on this.
I thought RCD's measured the balance between phase and neutral and tripped if their was an imbalance IE a phase or neutral earth fault only if the circuits are on, so how can an RCD trip if all the circuit MCB's it supplies are in the off position?
The electrician removed all the neutral wires from each circuit one by one until he found the circuit that was causing the RCD to trip, all this was done with the MCB's in the off position.
The main switch to the fuse board was in the on position.
Thanks.
 
Ok thanks for the replies I have read the thread.
The one thing that puzzles me is if you have an individul cable not connected to any other circuits just an RCD and mcb.
There is no possibility of leakage down the neutral from other circuits because this is just one wire supplying one circuit.
Let's say this wire supplies a lighting circuit.
The neutral and earth of this wire/ circuit are connected at the board as they should be but this is the only circuit supplied by this RCD.
You have the MCB switched off and you touch the neutral and earth wires of the cable/ circuit together.
Does this trip the RCD?
If it trips the RCD could someone please explain why?
It's very puzzling me.
Thanks.
 
Last edited:
Hi there, La Poste.

Although l cannot give you the answers, you are looking for, l am also eager to find out the answer, as l believe that l have activated an RCD in this way.

I was doing a job for a friend, the mcb was isolated, yet when l touched the neutral & earth wires together, of the circuit l was working on, l activated the RCD by doing so.

After putting this to my college tutor, he told me that this was impossible and that l must be mistaken.

I beg to differ with his explaination, as l activated the RCD with the circuit off on three different occasions. Please can anyone shed some light as to how this could happen?
 
Ok thanks for the replies I have read the thread.
The one thing that puzzles me is if you have an individul cable not connected to any other circuits just an RCD and mcb.
There is no possibility of leakage down the neutral from other circuits because this is just one wire supplying one circuit.
Let's say this wire supplies a lighting circuit.
The neutral and earth of this wire/ circuit are connected at the board as they should be but this is the only circuit supplied by this RCD.
You have the MCB switched off and you touch the neutral and earth wires of the cable/ circuit together.
Does this trip the RCD?
If it trips the RCD could someone please explain why?
It's very puzzling me.
Thanks.

I think the simplest way to explain it is that the neutrals of an installation are all connected together at some point - whether it be the neutral bar, the main isolator, whatever.

On that basis, if any circuit is closed (ie current flowing), then the current is returning down the neutral and heading for the supply transformer.

Even, as you describe, if you have one line conductor through the RCD, through an MCB (open), up to the load and then the neutral back to the RCD, the other side of the RCD is still connected to the other neutrals of the installation.

If you then introduce a N - E fault on your RCD circuit, you are introducing a parallel path back to the transformer via earth.

Any current flowing in other circuits via the neutral could flow up your isolated circuit's neutral and down to earth - if this current was more than 25/30 mA, then the RCD could trip, as it is only flowing in the neutral and not in the isolated line conductor - an imbalance:)
 
I tripped the RCD the other day for the same reason..


Thats why you must remove live, neutral, cpc and re connect cpc, neutral, live.

as YOU CAN GET A SHOCK FROM THE NEUTRAL

I think WayneL explained this in another thread the other day..


EDIT pennywise already linked it. lol
 
Last edited by a moderator:
The RCD works on the basic principle of electromagnetism. You have a live current, that goes through a coil on the RCD, generating a magnetic field (A), then to the load and returns on the neutral of the RCD producing a magnetic field (B) that is 180 degrees out of phase with the A. Therefore, A magnetic field is annulled by B magnetic field. Should there be a difference between the A and B, as it is an alternating current, it will produce a field that is proportional to the difference (C). If the current is big enough, it will produce a magnetic field C on a separate winding on the RCD solenoid that if big enough, it will cause the solenoid to activate or trip and cut the supply. Notice the statement big enough which is key to why your RCD is operating when you short N-E as there will always be a very small current present due to a potential difference between conductors or imbalances in transformer circuit.
 

Reply to RCD neutral fault. in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
486
Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top