hi to all i need a bit of help as i dont normally deal with 3 phase i have come to carry out a periodic inspection and carried out a rcd test on varrious circuits and it wont trip at 1x test

the system has a old mem d/b with a rcd as a main switch
what would cause the rcd not to trip out

thanks mike
 
does it trip at x5? are you sure it's 30mA.? if so, it's duff and needs replacing.
 
it says on the rcd 0.03ma on it and in fairness i carried out a auto test and it stopped at 1x due to it detecting a non trip
 
try it on manual. if it don't trip, press the test button. sometimes, if they've not been used they stick. if in doubt, replace.
 
well thats what i thought so i pressed the functual test botton but still no good do i only need to carry out the testing at 5x then
 
if it don't trip at X1 and don't trip off the test button, it'e deffo faulty. replace it.
 
that was my conclusion the problem is is a really old board so i think i would be easier to replace the whole thing it has 10 circuits at prescent but i have no idea how much to charge to replace it as its a church it has to go to a comittee for the go ahead
 
place rcd on floor, whack it with a hammer. then you are certain its duff. seriously, though, if you're considering replacing the whole board, cost out your materials, estimate the hours involved ( including testing) and multiply the hours by what you think is a reasonable hourly rate. then add on 25% for materials mark-up and snags.
 

Reply to rcd not tripping in the Electrician Talk | All Countries area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
303
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
284
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
356

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
604
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
638
davesparks
D

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top