N
nickblake
RCD tripping problem , i have installed a RCBO on a lighting circuit ,and the RCBO wont trip under test conditions , R1 R2 Reading was 0.58 Zs was 0.74 ,but when i test on 30 ma x 1 @180 degress the tester says its tripped in 30 ms but hasnt physically tripped , ive changed the RCBO and its still the same ,also connected the earth to an earth of another circuit and the RCBO trips ,testing it with the meter across the RCBO at the board it trips in 23 ms , all i can think of that there is an earth fault that is not showing up under normal test conditions but only showing when the RCD test is is carried out as the RCD test is testing the circuit under fault conditins am i correct in assuming there is an earth fault any ideas , meters fine tests Any onther circuit as all 14 are on RCBO's just the one that wont trip