RCD tripping problem , i have installed a RCBO on a lighting circuit ,and the RCBO wont trip under test conditions , R1 R2 Reading was 0.58 Zs was 0.74 ,but when i test on 30 ma x 1 @180 degress the tester says its tripped in 30 ms but hasnt physically tripped , ive changed the RCBO and its still the same ,also connected the earth to an earth of another circuit and the RCBO trips ,testing it with the meter across the RCBO at the board it trips in 23 ms , all i can think of that there is an earth fault that is not showing up under normal test conditions but only showing when the RCD test is is carried out as the RCD test is testing the circuit under fault conditins am i correct in assuming there is an earth fault any ideas , meters fine tests Any onther circuit as all 14 are on RCBO's just the one that wont trip
 
so do you mean the earth lead of the tester to aseperate RCBO all together? Or are you testing the original RCBO but connecting the earth lead to another circuits CPC?
 
no my friend just a normal switch MK grid switch its a wiard one i can tell you , every thing tests out fine R1 R2 are ok Zs is OK insulation resistance is over 200 meg , but wont trip the RCD on just this one circuit all the other RCBO's trip fine 24.6 ms to 28 .2 ms , there on lights and sockets , its just this one circuit real head scratcher to me all i can think is when the RCD tester puts the fault on the circuit the cable cant handle the fault current the RCD is not detecting the fault :rolleyes:
 
yes widdler its to the same RCBO but connected the earth to another circuit that just to prove that the RCBO is functioning with another earth
 
Last edited by a moderator:
no my friend just a normal switch MK grid switch its a wiard one i can tell you , every thing tests out fine R1 R2 are ok Zs is OK insulation resistance is over 200 meg , but wont trip the RCD on just this one circuit all the other RCBO's trip fine 24.6 ms to 28 .2 ms , there on lights and sockets , its just this one circuit real head scratcher to me all i can think is when the RCD tester puts the fault on the circuit the cable cant handle the fault current the RCD is not detecting the fault :rolleyes:

Mystified then:confused:
 
yes that was the first thing i did changed the RCBO ,also swapped the wire to another RCBO and it wont trip , it must be some thing with the earthing to that circuit but it all test out ok R1R2 fine IR all conductors above 200 meg ohm ,Zs fine just wont trip , think ill have to strip the circuit down and do RCD tests at every point on the circuit till i find the point where it stops tripping ,ive tried Zs and RCD at 4 of the 5 points and i doesnt trip its very wiard
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
RCD not trippng
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
11
Unsolved
--

Advert

Thread statistics

Created
nickblake,
Last reply from
nickblake,
Replies
11
Views
2,081

Advert

Back
Top