I have been asked to do a job to replace some damaged bollards at a hotel. The circuit in question has a few problems with bad terminations and high ZS readings which I hope to rectify. The one thing I am not sure is the fact that there is no RCD on the circuit. The MCB is overrated anyway which will need looking at but as I have not installed a new circuit or changed the existing what should I do. Do I have to put one in in this instance?

I am worried that the circuit would have nuisance tripping anyway if I fitted an RCD.


Cheers
 
Are the hotel owners likely to ask unqualified staff to drill into walls, I doubt it.
The requirement for RCD protection is mostly for domestic situations and socket outlets. For installations under the supervision of a skilled or instructed person or where only authorised equipment is used and only skilled persons will work on the building, RCD protection is not required.
 
If the cables are earth shielded and the Zs is OK then I don't think you would need to use RCD protection. (not 100% sure) However, as these lighting bollards outside and are often damaged, both accidentally and deliberately, I would want to use one.
 

Reply to RCD on an existing lighting circuit? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
642
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
961

Similar threads

No to all. Also would require a means of isolation for PIV - pulling a fuse wouldn't be acceptable. I don't mean to seem disrespectful, but this...
Replies
1
Views
1K
nicebutdim
N
Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
2
Replies
19
Views
956

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top