hello evryone, please can anyone tell me where a rcd be fitted on a three phase board. how would it be installed and what rating, please can explain as much as possible.

cheers everyone
 
Fit it in an enclosure adjacent to the DB but would like to ask why do you want to protect the whole installation this way as if it tripped you would loose everything thereby making any fault finding if it tripped really difficult.
 
Last edited:
Best have a read of section 704 in ol' red.

Socket outlets MUST have 30mA protection, then all other circuits have 300mA protection.

Easiest way is to have a 300mA RCD as the main incomer in the DB and then individual 30mA RCBO's for socket outlets.
 

Reply to rcd on three phase board in the Electrician Talk | All Countries area at ElectriciansForums.net

Similar Threads

Has the cover been removed, is it TP bussbar? I fitted one as @oscar21 linked to a few months ago, it was actually a nice board and with the TP...
Replies
5
Views
288
  • Question
Probably a bit late for the OP, but there's a very easy option if a manual solution is OK. Rotary cam switches are just the ticket - but not the...
Replies
4
Views
570
Sooo the client has accepted that we don't want to be fraudulently taking electricity so that worry is out of the picture. But now basically the...
Replies
32
Views
4K
  • Question
Agree with Dave disconnect unused Phases on the outgoing side of the isolator. No reason to replace mcbs with single pole, unless you need room...
Replies
2
Views
1K
  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
587

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks