Anyone got any thoughts on this....
TNS arrangement
ZE = 0.65 ohms
ZS on tested circuit 0.85ohms
RCD >1999 on 0.5 x
28 & 32 ish ms on 1 x
> 40 ms on 0 & 180 degs although the unit did pass on 0 degrees once or twice before failing the 180
Tested my Megger against a known good external RCD and changed batteries all to no
avail.
I haven't tested across the RCD directly as I didn't think to whilst on site but any suggestions would be most welcome.
The RCD is new as the old unit was giving 110ish ms on 1x and >40 ms on 5x so I assumed that it was this.
Thanks
CJ