Loooking for a bit of ideas on a issue if have with a RCD. 4 circuits on a submain that i recently changed, above the board was a leak so intally thought the problem was related to that. When carrying out the RCD auto test when it came to x1 the meter read error and would not trip. If i set it to x5 it tripped.
So put it down to a faulty RCD and changed it today, so when i auto tested this time it only goes and trips on x 1/2.
First off i checked my meter on another circut testing an RCBO on the main board which went fine.
So i disconnected all the loads on the problem board and tested individually but still the problem of trip on x 1/2. Next i disconnected the incoming supply and carried out a insulation resistance test 500v between conductors, no problem there.
I carried out a insulation test on the lighting circuit and had a reading of 0.04M between Live and Neutral but with all the lights as GU10 fluorescents would i be right in thinking the reading is down to this?
Anyway with the lighting circuit disconnected from the board still the RCD trips on x 1/2 so this has got me seriously scratching my head.
What i wondering is the board is the 3rd submain from the main panel and there is a 2 way RCD unit supplying a outside socket in the middle which im unsure where is fed from at this stage. Could this be a problem having another RCD downstream?
In the end put the old RCD back in tested that and is ok on x 1/2 but get the error message and no trip on x 1 again!!
Came away to get my thinking cap on and any help on what the problem may be?
The tester is a megger 1553 and was calabrated 6 months ago.
Any ideas gratefully accepted?
Cheers
So put it down to a faulty RCD and changed it today, so when i auto tested this time it only goes and trips on x 1/2.
First off i checked my meter on another circut testing an RCBO on the main board which went fine.
So i disconnected all the loads on the problem board and tested individually but still the problem of trip on x 1/2. Next i disconnected the incoming supply and carried out a insulation resistance test 500v between conductors, no problem there.
I carried out a insulation test on the lighting circuit and had a reading of 0.04M between Live and Neutral but with all the lights as GU10 fluorescents would i be right in thinking the reading is down to this?
Anyway with the lighting circuit disconnected from the board still the RCD trips on x 1/2 so this has got me seriously scratching my head.
What i wondering is the board is the 3rd submain from the main panel and there is a 2 way RCD unit supplying a outside socket in the middle which im unsure where is fed from at this stage. Could this be a problem having another RCD downstream?
In the end put the old RCD back in tested that and is ok on x 1/2 but get the error message and no trip on x 1 again!!
Came away to get my thinking cap on and any help on what the problem may be?
The tester is a megger 1553 and was calabrated 6 months ago.
Any ideas gratefully accepted?
Cheers