ash_s3
Hi all
installed some downlights for a customer the other day, nice easy job (as they all start out to be)
did the usual tests, Earth loop was a high reading, checked supply and it was TT even though a lead sheathed underground supply cable.
Ze was high 290ohms, bonding to gas and water all good 10mm which was bringing the zs down a fair bit.
suggested we try and get dno to change to tn-cs or if not possible we will get a better reading on a new rod.
Heres the headscratcher..
RCD as main switch, non split load DB, although fairly new Crabtree star breaker setup.
With all loads switched off the RCD will not test, will not trip at 1x or 5x or ramp test.
Tried brand new RCD, exactly the same. Disconnected the neutral fly lead from RCD and it trips perfectly within the permitted times.
I then went through each neutral one at a time disconnecting them and testing the RCD, found that with one ring finals neutrals take out it tests fine, turns out it's not a complete ring, line is ok but high resistance on neutral end to end.
Further investigation required but couldn't figure out why this would stop the RCD from operating.
The guy that changed the DB obviously had no tester as its a right cock-up but that's another story..
installed some downlights for a customer the other day, nice easy job (as they all start out to be)
did the usual tests, Earth loop was a high reading, checked supply and it was TT even though a lead sheathed underground supply cable.
Ze was high 290ohms, bonding to gas and water all good 10mm which was bringing the zs down a fair bit.
suggested we try and get dno to change to tn-cs or if not possible we will get a better reading on a new rod.
Heres the headscratcher..
RCD as main switch, non split load DB, although fairly new Crabtree star breaker setup.
With all loads switched off the RCD will not test, will not trip at 1x or 5x or ramp test.
Tried brand new RCD, exactly the same. Disconnected the neutral fly lead from RCD and it trips perfectly within the permitted times.
I then went through each neutral one at a time disconnecting them and testing the RCD, found that with one ring finals neutrals take out it tests fine, turns out it's not a complete ring, line is ok but high resistance on neutral end to end.
Further investigation required but couldn't figure out why this would stop the RCD from operating.
The guy that changed the DB obviously had no tester as its a right cock-up but that's another story..