This is a bit of a mad one and left me scratching my head big time!

just finished a rewire of a 2 bed property and carried out a full installation test, now all tests were satisfactory including the rcd tests......but earlier on in the job i went through an old existing cable whilst chasing and the rcd on the old existing board didnt trip, i thought nothing of it at the time but out of curiosity really i flashed an earth across a neutral today on the new installation and still got nothing from even the new rccbs

so after a while of investigating i found that the rccbs would only respond every now and again (more not working than working), so thinking the rccbs were faulty even though they tested fine using an rcd tester i decided to replace them but it was still in the same situation as before

any ideas anyone??

all rccb links were present and correct inside the board

there is an existing main earth with a ze of 0.20 (tnc-s system)
 
I would go with the rcd tester resuts
When you flash neutral to earth,you would still require the leakage current from somewhere for it to trip


If there are loads in circuit when they are flashed,it might then come out
With small leakage or fault currents it may never do so
 

Reply to Rcd Problems in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
264
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
740

Similar threads

  • Question
none at all.... and the rcd trips within specification... test button operational.... nothing to suggest there's a problem until you take the...
    • Like
Replies
2
Views
613
  • Question
Yea all out circuits were disconnected & Rcd ramped tested Think this will be the right way forward,with EL clamp meter Cheers have a nice Christmas 😎
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top