Rcd protection for domestic inatalls. | on ElectriciansForums
Discuss Rcd protection for domestic inatalls. in the Domestic Electrician Forum area at ElectriciansForums.net
APE37
Herts
Hi guys. Am I right in interpreting the regs with regards to rcds that they need to be rated equal to or higher than the main supply fuse? So not to overload them? Or am I reading it wrong?
Thanks on advance.
Thanks on advance.
That's my understanding of the regs now that's why in a split RCD consumer unit Hager are fitting 100A RCD's by default.
So for reference,
If you have a 100a main tncs supply and a 100a main switch and 2 rcds of 63 amps then this complies? I thought that the rcds would need to be 100a so to not overload them? Just looking at boards in catalogues and noticed that the boards come with 2 63a rcds or 80a rcds and couldn't see how these still comply the only board I can see comply is hager.
The trouble is only hager have done this and none of the other manufacturers seem to have followed suit. So cant see how they comply?
It's up to the installer how the install complies. A total potential load after the RCD less than the rating of the RCD will comply. If the potential load exceeds the rating of the RCD, an OCPD before the CU less than the rating of the RCD will comply.
But what if customer dont/want the cost of rcbos
Sell the RCBO's... we are electricians and we know what is right. Split load boards belong in the 80's. Things have changed, DC leakage current / electronic equipment. I don't compete with the flooding of the market with ÂŁ60 complete (split load AC RCD's) boards. Explain the difference - give the option and if they want to fit the cheap board - find someone else to do it.
Reply to Rcd protection for domestic inatalls. in the Domestic Electrician Forum area at ElectriciansForums.net
By retired electrician, I mean that I have retained my ticket but no longer do installation work. Thanks for the clarification. I missed that it...
From the title and first post it is not clear whether you are looking to install surge protection or a lightning protection system (LPS) or is it...
