i remember reading in the regs that a amoured cable does not need rcd protection is this right as i cant find the reg for it anywere. i am looking at running a amoured to a shed for a socket and light

cheers
 
Regulation 522.6.5 (ii) and 522.6.6 (i).

As your feeding a socket outlet from the SWA you might want to protect that socket under 411.3.3 by either fitting an RCD at the origin of the circuit or by fitting a BS 7288 RCD socket outlet.

If your earthing system is a TT you may find though that your unable to conform to the disconnection times with just an ordinary protection device due to the normal Ra value of the rod, and so would need to provide an RCD as additional protection
 
Unless your SWA is part of a TT system then there is no need to RCD protect the cable under any conditions outside or in, providing your not needing it for additional protection becasue as I said in my post you can't conform to the disconnection times becasue of a high Ra.

Under regulation 411.3.3 the socket is what requires the RCD protection and that can be achieved by a BS 7288 RCD socket.
 

Reply to rcd protection on a armoured in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
400
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
986
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I think I've found the answers to my questions... I can just do a straight forward wiring i.e. connect the 3 wires from the armoured cable to...
Replies
7
Views
1K
I assume said contractor is part of a Part P scheme (NICEIC, Napit, few others..) in which case complain to them. They'll investigate (in theory)...
Replies
10
Views
920

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top