RCD Protection on a PVinstall | on ElectriciansForums

Discuss RCD Protection on a PVinstall in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

I

ian81

Hi, can anyone help at all. Ive heard a few people say they dont put thier PV installs on an RCD, however am i correct in saying that under 17th edition everything should be RCD protected? If im being stupid please feel free to tell me incase ive missed something somewhere!!

Cheers in advance
 
No you are not correct.

However you will need to specifically design out the requirement for an RCD otherwise you are likely to need one.

More info coming soon about this next point:

If you are using ANY make of TL inverter, you will not be able to install it in a situation where a 30mA RCD is required.

So if you MUST have a 30mA RCD, then you will almost certainly have to install a transformed inverter.
 
In somecases weve used a garage unit with a 100mA rcd and ran armoured cable because weve used a sunnyboy 4000tl. It was just someone said to me that the PV course theyd done they was told to not install the system on an RCD.
 
If your 100mA RCD that you installed is a Type A then you may just as well not have installed it at all.

If the Array has any DC leakage at all (over 25 years a fault could develop) then the RCD will not trip even under 300mA of AC leakage.
 
Under DC fault conditions any RCD apart from a type B will be useless, it could become saturated and may not trip. If you need to protect your AC circuit using an RCD then as Worcester says design out the need for a RCD. You could use a Type B 30ma, but you run the risk of nuisance tripping.

Any installer / designer who relys on the inverters having inbuilt type B protection could be leaving themselves wide open in the event of DC faults.
 
Many valid points here, I think a definitive statement that might help clarify some of the above might be useful for those on this forum reading this, and other RCD threads. I can provide technical/supporting info if that is of any use?
 
if its a tt system whatever the inverter 100ma required for surface wiring 30ma for cables burried within fabric of building unless protected by swa or steel etc
tncs or tns no rcd required for surface wiring but as above again for burried.
 
I don't think the 15mA test current testers were very popular as that didn't correctly test the integrity of the system. I seem to remember my tester using DC to overcome problem tripping during testing. Although now I'm struggling to work it out in my head.
 
TL inverter on a TT system then will need a Type B RCD.

Andy - we could do with that decision tree!
 
I don't think the 15mA test current testers were very popular as that didn't correctly test the integrity of the system. I seem to remember my tester using DC to overcome problem tripping during testing. Although now I'm struggling to work it out in my head.

I use a Megger 1552 which is possibly one of the most popular multifunction testers available. That uses a test current of 15mA to avoid tripping 30mA RCD's on the low current loop (no trip) setting.
 
Last edited by a moderator:
Type A 100mA Rcds can be used on Inverters which by construction/ design are not capable of feeding in Dc injection currents to the grid Reg 712.411.3.2.1.2 identical wording to this in some Inverter manufacturers info
so check the manufacturers instructions for example SMA 4000tl Type A Rcd can be used
 

Reply to RCD Protection on a PVinstall in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hope everyone has had a great Christmas and here’s hoping we all have a better new year coming our way ! Remember our riches aren’t measured by...
    • Friendly
    • Like
Replies
11
Views
567
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
760
  • Sticky
  • Article
Thanks so much for sharing this with us! I’ll definitely take a look, it seems like there are a lot of useful and interesting products. The idea...
    • Like
Replies
5
Views
2K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
1K
I don't think I'd use it mate even the one line heading then one long paragraph screams ai. And untrustworthy. I don't think much has been edited...
    • Optimistic
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top